Symmetra Power Array Charging Wattage
What is the maximum charging wattage that i can get from a symmetra power array. currently i am getting aprox 1200 watts (9.8 amp).
My UPS has following Specs:
4 power modules (4kva each)
1 Internal battery module
an external battery bank with 490 AH cells.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:38 AM
i asked the technical support lead for the Power Array which is the older beige model UPS, not the newer LX.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
it is about ~300 watts when i checked so your reading appears correct. if you need it to charge faster, you can add another power module to get the another ~300 watts.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
Are you sure about that wattage give me a call which ups are youy using the LX or the older one 775-888-8788
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
You are right, the older power array models have 300 watts per module. i verified it by inserting the fifth module and charging current bumped to 12.7 amps which is approx 1500 watts. i have a few of these models and all show the same charging characteristics.
Thanks for the quick and correct information.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:39 AM
no problem 🙂
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:45 AM . Last Modified: 2024-03-11 03:38 AM
i asked the technical support lead for the Power Array which is the older beige model UPS, not the newer LX.
Link copied. Please paste this link to share this article on your social media post.