Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:47 AM . Last Modified: 2024-03-19 01:52 AM
Our preventive maintenance program requires a 30 minute battery discharge test every 6 months on our UPS system. What would be the recommended procedure for doing this? I'm new to the work site and have not went thru this test before. I've heard that the last time this was tried by tripping the fed breaker, there were problems during the test and bringing the system back online. We have generator controls, monitoring systems, fire/gas systems and lighting being fed from the UPS. The manuals I've read on board list a "simulate power failure" option in the menu, but I have read in the forum that this is only for a few minutes. Any help and recommendations would be appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:47 AM . Last Modified: 2024-03-19 01:52 AM
Hi,
A 30 minute test is a long time for batteries and would degrade the life of the batteries. If you wanted to just run on the batteries without the generator or utility available you could open Q1 which would force the unit to battery.
The battery self-test simulates a power failure and the UPS will run on battery for 1 minute or 10% of the available runtime. In this situation the utility is still available.
If you require assistance you should contact local 3 phase technical support. Local support can be found at this link http://www.apc.com/au/en/support/contact-us/index.jsp
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:47 AM . Last Modified: 2024-03-19 01:52 AM
Hi,
A 30 minute test is a long time for batteries and would degrade the life of the batteries. If you wanted to just run on the batteries without the generator or utility available you could open Q1 which would force the unit to battery.
The battery self-test simulates a power failure and the UPS will run on battery for 1 minute or 10% of the available runtime. In this situation the utility is still available.
If you require assistance you should contact local 3 phase technical support. Local support can be found at this link http://www.apc.com/au/en/support/contact-us/index.jsp
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.