Symmetra PX & Serial Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX & Serial Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Ratso_apc
Crewman Ratso_apc
Crewman

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
7
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

Symmetra PX & Serial Shutdown

Greetings -

I recently inherited a small data center with a Symmetra PX 80kW (208V 3PH). While I have over 15 years experience with the Smart-UPS line, this is the first Symmetra I've had.

I'm trying to find a mechanism to automatically shut down key servers via their serial (or USB) port, but my read of the docs indicates the Symmetra PX does not provide this functionality. This seems strange for such a high-end device, so I'm hoping I'm just missing something.

At one point the "Synchronized Control Group" functionality looked promising, and I considered network-connecting a Smart-UPS to the Symmetra PX and placing them into a Synchronized Control Group. That way, when the Symmetra triggered a low-battery condition, the Smart-UPS could in turn be used to trigger the serial shutdown via an attached Share-UPS. But the docs indicate that all UPS's in the Control Group MUST be of the same model (with no reason given). So it appears that approach may not work.

Any advice on how to affect a serial-driven automatic shutdown with the Symmetra PX would be greatly appreciated.

Thanks,
Ratso

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

I don't see Xeon processors on the compatibility list either:

http://www.apcmedia.com/salestools/ASTE-6Z5QEX_R0_EN.pdf

I would suggest installing the PCNS software on a machine running a 32 bit supported OS. When you log into the web interface of the PCNS client, not the network card, you can configure that machine to execute a command file for a certain condition. To do this, open a web browser and type http://ipaddress:3052 (use real ip as opposed to words). From here you would configure an event, for example, UPS on battery. When the UPS has been on battery for X number of seconds, execute this command. The command file can be a simple batch file that sends a shutdown command to the 64 bit OS's. This would be a valid workaround to the 64 bit support issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Ratso_apc
Crewman Ratso_apc
Crewman

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

Greetings -

I recently inherited a small data center with a Symmetra PX 80kW (208V 3PH). While I have over 15 years experience with the Smart-UPS line, this is the first Symmetra I've had.

I'm trying to find a mechanism to automatically shut down key servers via their serial (or USB) port, but my read of the docs indicates the Symmetra PX does not provide this functionality. This seems strange for such a high-end device, so I'm hoping I'm just missing something.

At one point the "Synchronized Control Group" functionality looked promising, and I considered network-connecting a Smart-UPS to the Symmetra PX and placing them into a Synchronized Control Group. That way, when the Symmetra triggered a low-battery condition, the Smart-UPS could in turn be used to trigger the serial shutdown via an attached Share-UPS. But the docs indicate that all UPS's in the Control Group MUST be of the same model (with no reason given). So it appears that approach may not work.

Any advice on how to affect a serial-driven automatic shutdown with the Symmetra PX would be greatly appreciated.

Thanks,
Ratso

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

Hello Ratso,

Due to the size of the Symmetra 80K, it is adviseable that you use Powerchute Network Shutdown as your server shutdown software. Each Symmetra should have a Network Management Card (AP9617 or AP9619) installed. You can assign an IP address to this card and your Symmetra is now accessible over the network. Once the card is on the network, you can install Powerchute on each of the servers that you would like to have shutdown on a power failure event. This software doesn't communicate over a serial cable but via the network. I understand that you would like to use a serial cable, but the serial based Powerchute software (Powerchute Business Edition) is only tested on smaller single phase UPS units, such as the Smart UPS.

You can download Powerchute Network Shutdown from the following link.

http://www.apcc.com/tools/download/software_comp.cfm?sw_sku=SFPCNS221&id=127&family=&part_num=&swfam...

Reply

Link copied. Please paste this link to share this article on your social media post.

Ratso_apc
Crewman Ratso_apc
Crewman

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:30 AM . Last Modified: ‎2024-03-19 01:47 AM

Thanks for the timely response KVM4Life -

I'm familiar with the PCNS software, but I don't subscribe to the network-based shutdown philosophy, at least not until PCNS supports certificate-based authentication for its network traffic. That's one reason why I'm looking for a serial-based mechanism.

You state that "Due to the size of the Symmetra 80K, it is adviseable that you use Powerchute Network Shutdown as your server shutdown software."

While I don't see how the capacity of the UPS would affect the mechanism it uses to trigger a shutdown, the statement raises a more relevant question: By "advisable" do you mean to say that it's not possible to do so? I accept the fact that you (or APC?) may advise against it, but the original question remains: Is there a way to do it?

Oh yes, just to clarify: I don't (historically) use the PowerChute Business Edition software for sensing the serial trigger. I use the native serial-sensing mechanism that's typically part of the OS distribution (e.g. Win2003, Linux).

Respectively,
Ratso

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

Hello,

Okay, let me clarify. Powerchute Business Edition is not tested on Symmetra products. Powerchute Network Shutdown is the advised software due to the fact each unit is shipped with a Network Management Card.

The reason I mentioned the size of the UPS is because its an 80KVA unit 80KVA can support a large number of servers (100+ and more). If you were to try and gracefully shutdown all these servers, you would need several serial connections, which could take up a lot of space. Also, the maximum number of servers that you can shutdown off of a serial connection to one UPS is 40 through our Share UPS product line.

I apologize if I can't provide you a better answer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

Hi Ratso,

Sounds good. I meant it as the software is tested on Smart UPS units or devices in Simple signaling. Symmetras are seen as supporting larger loads, and with regards to servers, you could potentially plug in a high number of servers that would generally create a mess in terms of the number of required serial cables.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

I run a couple of small server rooms with 12kva Symmetras. We recently upgraded our server and OS architecture to I am using 64-bit Xeon processors and 64-bit Windows OS. My issue with Powerchute is the lack of 64-bit support. The only 64-bit Powerchute available is for Itanium processors.

Theoretically the 32-bit powerchute will work, but I am having installation issues and support is telling me that while it might work, it is not actually supported. What are my options for clean shutdown of 64-bit Xeon systems if I am using a Symmetra?

Chad

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:31 AM . Last Modified: ‎2024-03-19 01:47 AM

I don't see Xeon processors on the compatibility list either:

http://www.apcmedia.com/salestools/ASTE-6Z5QEX_R0_EN.pdf

I would suggest installing the PCNS software on a machine running a 32 bit supported OS. When you log into the web interface of the PCNS client, not the network card, you can configure that machine to execute a command file for a certain condition. To do this, open a web browser and type http://ipaddress:3052 (use real ip as opposed to words). From here you would configure an event, for example, UPS on battery. When the UPS has been on battery for X number of seconds, execute this command. The command file can be a simple batch file that sends a shutdown command to the 64 bit OS's. This would be a valid workaround to the 64 bit support issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now