Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-04 05:18 AM
HI.
Randomly I get a low and/or critical output voltage alarm on L1.
There is no physical problem i dont believe as if I meaure the outputs there are ok. all around 240V. But L1 output reports 120, 140,155 and so on. Jumps around. A good whack on the side on the unit makes it jump around.....
THen all of a sudden after some time it will go back to reporting 240v. on the L1 output.
I have tested numerus time and the actual L1 output is solid at 240v where it should be.
I have managed to disable / change the threshold settings so at least the critical alarm and beep is gone, but i would like to get it sorted. I have checked the sensors on the back busbars and they seems to be firmly connected.
Any ideas?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-29 12:57 AM
Hi @Brukutu
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. A[ologies for the late revert, would you happen to know if the UPS has an active service contract with us? I believe that a Field Service Representative is one of the best ways to address this issue as they can do a technical check on the UPS and its components.
If you are familiar with the LCD of this unit, kindly go to UPS > UPS Status and then UPS Tests and Diags. I would like to check if you can grab the raw status data (RSD) from the unit and we'll check if it would show any fault/issues that fit your description.