Symmetra PX 80 kVA Inactive Power modules?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 80 kVA Inactive Power modules?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:27 AM

0 Likes
5
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:27 AM

Symmetra PX 80 kVA Inactive Power modules?

I have a APC Symmetra PX 80kVA (SYCF80KF) with 9 Power Modules (SYPM10KF) as well as 2 Intelligence Modules (SYM1M4). Is there any way to test the power modules as it stands without any batteries connected? I have finally figured out how to locally remote with the Serial Cable (had to disconnect Display cord) but can not see any of the other modules. Any help with this topic would be very helpful.

Thank you,

Dru

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Alrighty.

You have an AP9617 Network Management Card which is accessible via HTTP, HTTPS, FTP, telnet, ssh, etc. When you log in via serial cable, you have a menu driven interface. What you'd do if you do not want to just assign it an IP address is go to the device manager menu (option 1 and press enter) and in there it should say something similar to Symmetra PX 80K and you press 1 for that and then you'll be in the menu where most of the UPS information is. You just press the numbers for the options you want.

Alternatively, I'd recommend you just put an IP address on it quickly (even if temporarily just to view it easier and you do a direct connection with a crossover cable to the ethernet jack). From the main menu, go to network->TCP/IP and in there you can use DHCP, BOOTP, or manual IP settings and the menu will help you through it somewhat. This set up for TCP/IP settings is outlined here (refer to NMC1 instructions and you are already doing the local console/serial method): How do you make a Network Management Card communicate on a network? | FAQs | Schneider Electric US

When you log in via the web, its a bit quicker to navigate and check out your UPS status, voltages, etc and even maybe other stuff down the road (email notifications, SNMP, RADIUS, etc).

Let me know if you have any more questions based on that. smile

I forgot - I am not an expert on the UPS but once I can see the management card or walk you through what to look at once we look in the right spots, I can help you or get someone to help us further to see what state the UPS is in. Perhaps the output is commanded off or it is in bypass or something.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Hi again Dru

I can tell from what you've provided that there is no communication between your management card and UPS. The management card itself is fine though most likely so we need to figure out what is causing the communication loss (it could be the fact that UPS itself is completely dead as far as communications go because of the state it is in but I am not sure). That is why you see no UPS information. You also have older firmware that I'd like to update at some point.

Either way, I am a little out of my league with this UPS and the specifics to communication to the AP9617 based on what you've said so far and the screenshots I am seeing.

Would you be willing to contact our 3 phase UPS support via phone to have them check a few things with you that are specific to the UPS that could cause this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

I have a APC Symmetra PX 80kVA (SYCF80KF) with 9 Power Modules (SYPM10KF) as well as 2 Intelligence Modules (SYM1M4). Is there any way to test the power modules as it stands without any batteries connected? I have finally figured out how to locally remote with the Serial Cable (had to disconnect Display cord) but can not see any of the other modules. Any help with this topic would be very helpful.

Thank you,

Dru

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Hello,

Could you clarify - are you logging into the Network Management Card (comes preinstalled in the management card) and finding some of the power modules say "inactive" or similar? Could you clarify? Have you accessed the web interface of the management card at all via IP? I ask because it'd be helpful to perhaps review the log files or provide screenshots so we could better understand the question.

If the UPS is turned on and outputting power while "online," regardless of your load, all of them should be operational.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Hi Angela,

I am logging into the "Computer Interface" module on the front of the APC unit. (See attached screen shots) ( & I am new to this product line and I am not familiar with the web interface and have not been able to find any information on it).  When I log into to the unit, I do not see the power modules at all, not sure if I am looking in the right place or not. Also the fans are not running on the power modules, thought this may be due to not being hooked up to any batteries at the moment??? They are just stand alone units for now.

These were given to us and we would like to see if they are fully operational before we include them on our network.

Thank you,

Dru1357_SP32-20130805-161943.jpg1358_SP32-20130805-162002.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Alrighty.

You have an AP9617 Network Management Card which is accessible via HTTP, HTTPS, FTP, telnet, ssh, etc. When you log in via serial cable, you have a menu driven interface. What you'd do if you do not want to just assign it an IP address is go to the device manager menu (option 1 and press enter) and in there it should say something similar to Symmetra PX 80K and you press 1 for that and then you'll be in the menu where most of the UPS information is. You just press the numbers for the options you want.

Alternatively, I'd recommend you just put an IP address on it quickly (even if temporarily just to view it easier and you do a direct connection with a crossover cable to the ethernet jack). From the main menu, go to network->TCP/IP and in there you can use DHCP, BOOTP, or manual IP settings and the menu will help you through it somewhat. This set up for TCP/IP settings is outlined here (refer to NMC1 instructions and you are already doing the local console/serial method): How do you make a Network Management Card communicate on a network? | FAQs | Schneider Electric US

When you log in via the web, its a bit quicker to navigate and check out your UPS status, voltages, etc and even maybe other stuff down the road (email notifications, SNMP, RADIUS, etc).

Let me know if you have any more questions based on that. smile

I forgot - I am not an expert on the UPS but once I can see the management card or walk you through what to look at once we look in the right spots, I can help you or get someone to help us further to see what state the UPS is in. Perhaps the output is commanded off or it is in bypass or something.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore