Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Hello,
As part of MGE Galaxy 3500 15kVA 400V 3:1, Start-up 5X8,
Reference: G35T15K3IS.
I wish batterr on battery rack.
I have two questions:
1.
When I look at the documentation for the battery circuit breaker SUVTBB10K20H , I do not see coil tripping? Is this normal?
Should add one coil?
What type?
2.
How the Galaxy is reacting when we have a emergency stop, the DC bus is disconnected from the rest of the UPS?
How ?
Thank you in advance for your answers. ![]()
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Hello,
As part of MGE Galaxy 3500 15kVA 400V 3:1, Start-up 5X8,
Reference: G35T15K3IS.
I wish batterr on battery rack.
I have two questions:
1.
When I look at the documentation for the battery circuit breaker SUVTBB10K20H , I do not see coil tripping? Is this normal?
Should add one coil?
What type?
2.
How the Galaxy is reacting when we have a emergency stop, the DC bus is disconnected from the rest of the UPS?
How ?
Thank you in advance for your answers. ![]()
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:57 AM . Last Modified: 2024-03-19 12:26 AM
Hello,
As part of MGE Galaxy 3500 15kVA 400V 3:1, Start-up 5X8,
Reference: G35T15K3IS.
I wish batterr on battery rack.
I have two questions:
1.
When I look at the documentation for the battery circuit breaker SUVTBB10K20H , I do not see coil tripping? Is this normal?
Should add one coil?
What type?
2.
How the Galaxy is reacting when we have a emergency stop, the DC bus is disconnected from the rest of the UPS?
How ?
Thank you in advance for your answers. ![]()