Hi, can any one explain B1,B2 and C in attached picture
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
Hi Adnanmian,
B1, B2, and C are installation methods (cable types etc) defined by the IEC. The specifics can be found in IEC section 60364-5-52. Unfortunately I am not able to provide you with the actual IEC document.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
Hi Adnanmian,
B1, B2, and C are installation methods (cable types etc) defined by the IEC. The specifics can be found in IEC section 60364-5-52. Unfortunately I am not able to provide you with the actual IEC document.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
thanks for help
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:59 AM . Last Modified: 2024-03-19 12:25 AM
I am 99% sure that the "mm 'squared'" notation refers to the cross sectional area of the conductors connecting the ups to the electrical distribution...( which in turn refers to wire gauge). Below that header are the values are shown for either single or double lugged interconnects to the main / bypass / etc inputs and outputs on the UPS.