Hi, I want to know if a SY200K250D can be expanded to a 250kVA/KW configuration and what modules would I have to add?
Or do I have to change frames and go with the SY250K500D?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
You should have at least 1.6 batterymodules (1 module = 1 row = 6 units) per powermodule.
So, 10 powermodules require minimum 10 x 1.6 = 16 modules = 2 full battery frames.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
So long as your site wiring was for the 250kw load, it should have two empty slots for 25KW modules.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Yes i can be expanded upto 250kVA/KW . But if your load will be between ( 225-250KVA/KW) then it will not be internal redundant.
You simply need to add SYPM25KD Qty 02/-
Here is link for more information
http://www.apc.com/shop/pk/en/products/APC-Symmetra-PX-25kW-Power-Module-400-480V/P-SYPM25KD
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Thanks for your reply.
Do I need to add any battery modules?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
You should have at least 1.6 batterymodules (1 module = 1 row = 6 units) per powermodule.
So, 10 powermodules require minimum 10 x 1.6 = 16 modules = 2 full battery frames.
Link copied. Please paste this link to share this article on your social media post.