Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-26 05:12 AM . Last Modified: 2024-03-19 01:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:12 AM . Last Modified: 2024-03-19 01:04 AM
Hi!
I've got a Symmetra PX 16kW UPS and Automatic Fire Extinguish System in server room. After signal from Fire System, all InRow coolers are going to standby mode. After that there is a danger of servers overheating. I've got an idea to connect Fire System to UPS. I know it's possible thru EPO Control in UPS but it is an emergency power off without any delay. I'm wondering is it possible to somehow connect Fire System to UPS and send an Powerchute signal to servers after fire alarm? Thx for any suggestions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:12 AM . Last Modified: 2024-03-19 01:03 AM
maybe i missed something but if the EPO signal is sent to the UPS, it will be sent an immediate signal to shutdown, and thus drop the load and not have time to send a signal to any of the powerchute clients since that is how the EPO works because of fire code.
i guess what else you could be referring to is connecting the EPO to a dry contacts management accessory which probably wouldnt pass any local codes or anything but would probably be feasible to trigger a shutdown. we'd need a network management card with dry contacts (AP9631+AP9810) or AP9610 or AP9619 if you have one already and powerchute network shutdown.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:12 AM . Last Modified: 2024-03-19 01:03 AM
maybe i missed something but if the EPO signal is sent to the UPS, it will be sent an immediate signal to shutdown, and thus drop the load and not have time to send a signal to any of the powerchute clients since that is how the EPO works because of fire code.
i guess what else you could be referring to is connecting the EPO to a dry contacts management accessory which probably wouldnt pass any local codes or anything but would probably be feasible to trigger a shutdown. we'd need a network management card with dry contacts (AP9631+AP9810) or AP9610 or AP9619 if you have one already and powerchute network shutdown.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.