Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Symmetra LX - All Battery Modules Fail

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX - All Battery Modules Fail
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
1
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

Symmetra LX - All Battery Modules Fail

Back in 2009, after happily running our Symmetra LX UPS for a couple years, the unit performed one of it's bi-weekly self tests and low and behold it found ALL four battery modules were bad. Incredulous, we opened a case with APC. Surely, all four SYBT5 battery modules could not have gone bad at once! What's the point of having individual hot-swap modules, if all of them go bad at once, leaving the load unprotected. APC technicians didn't seem to believe it either, and proceeded to drag us through a firmware upgrade and dump of MIM data to analyze the system. However, when all was said and done, they agreed that it was just a case of "bad luck" and that all the batteries were indeed bad and needed to be replaced. At great expense we had 4 new SYBT5 modules shipped 2-day, and was left to operate the load for 2 days without protection. Oh well, must have been sun spots. . .

Except, now it's 2011. . . We had a 10 minute power outage Friday night which was handled perfectly by the Symmetra. Critical load never went down. But, 1/2 an hour after the power was restored ALL FOUR battery modules are again reporting bad. Again, my critical load is unprotected while we wait for battery modules to be rapid shipped (at a ransom).

Apparently, I'm an idiot for thinking that the battery modules should fail sequentially, thus giving you the opportunity to replace a single module while still protecting the load (albeit at a decreased runtime).

APC recommends SYBT5 modules should not be stored uncharged for longer than 6 months. So, I can't stockpile the modules for 2 years, while I wait for this to happen again. So, what should I do?

1. Just get in the habit of buying 4 new SYBT5 modules every 6 months?
2. Periodically replace "some" number of good SYBT5 modules in the frame so all four are not the same "age" and there is always a mix of newer and older batteries?
3. Look for a new UPS solution?

Thanks,
Patrick

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

What you say is probably true. Even though the UPS is reporting all four batteries failed, there is actually a little life left in them, and it would protect the load, albeit at a decreased runtime. It is a real shame the user isn't given this information. Instead of "battery degraded - decreased runtime!," we get "batteries failed - 0 min runtime!" - accompanied by incesent beeping and sending alert emails every 30 seconds. It tends to make you freak out!

It's also a shame that there is no battery calibration information available to the user. You say each battery stores calibration information. Why are users not entitled to see this on a module by module basis? Wouldn't this give the user some valuable predictive information on which battery module may be getting weak. Thus, allowing us to replace proactively? Why hide behind the jumble of cryptic "raw data?" I mean, other than to protect APC's support revenue streams?

Heck, for that matter why forbid the SYBT5 units to be re-leaded? Why put some silly "obsolescence" chip in the unit to permanently render the module useless, even though the cells have been replaced? Why can't it be recalibrated? It's obviously designed to protect APC's revenue, not to protect customers. I can locally source cells, in an emergency.

As for the extended warranty. . .
It makes me think of an expensive Maserati, which is a great car as long as you take your Italian mechanic everywhere you go. Why should I have to pay for extra support to manage what (at the time of the sales pitch) was touted as field replaceable modules? It would be like buying expensive maintenance on a printer to help you replace toner cartridges? Again, I fully expect battery modules to fail, just not all at once!

Thankfully, our new battery modules arrived today and they are in and running. Since it seems that we only get two years out of them, I have made a note to replace at least one every year, regardless of whether they test 'OK." This way, we'll always have a variety of battery ages. Hopefully, this hedges against having all the batteries fail simultaneously.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
0
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

What you say is probably true. Even though the UPS is reporting all four batteries failed, there is actually a little life left in them, and it would protect the load, albeit at a decreased runtime. It is a real shame the user isn't given this information. Instead of "battery degraded - decreased runtime!," we get "batteries failed - 0 min runtime!" - accompanied by incesent beeping and sending alert emails every 30 seconds. It tends to make you freak out!

It's also a shame that there is no battery calibration information available to the user. You say each battery stores calibration information. Why are users not entitled to see this on a module by module basis? Wouldn't this give the user some valuable predictive information on which battery module may be getting weak. Thus, allowing us to replace proactively? Why hide behind the jumble of cryptic "raw data?" I mean, other than to protect APC's support revenue streams?

Heck, for that matter why forbid the SYBT5 units to be re-leaded? Why put some silly "obsolescence" chip in the unit to permanently render the module useless, even though the cells have been replaced? Why can't it be recalibrated? It's obviously designed to protect APC's revenue, not to protect customers. I can locally source cells, in an emergency.

As for the extended warranty. . .
It makes me think of an expensive Maserati, which is a great car as long as you take your Italian mechanic everywhere you go. Why should I have to pay for extra support to manage what (at the time of the sales pitch) was touted as field replaceable modules? It would be like buying expensive maintenance on a printer to help you replace toner cartridges? Again, I fully expect battery modules to fail, just not all at once!

Thankfully, our new battery modules arrived today and they are in and running. Since it seems that we only get two years out of them, I have made a note to replace at least one every year, regardless of whether they test 'OK." This way, we'll always have a variety of battery ages. Hopefully, this hedges against having all the batteries fail simultaneously.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of