Installing APC static switch to bottom of Symmetra PX 80k

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Installing APC static switch to bottom of Symmetra PX 80k
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
1
1501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

Installing APC static switch to bottom of Symmetra PX 80k

Looking for some step by step instructions on how to swop SS over part number SYSW80kH APC for a Symmetra PX 80k


this is what i know so far off my top of me head or just check thou thanks.

1. Transfer the UPS to static bypass, and then bypass externally. Shut down the UPS and the static switch is replaced with the UPS powered off.
2. Turn the Static switch enable locking latch (with arrow pointing towards module)
counterclockwise until it points downward. This will disable the static switch module.
3. Remove the four screws which secure the static switch module in the enclosure.
4. Withdraw the static switch module by pulling on the handle and remove the static switch
from the enclosure.
5. Remove the retaining screw for the System ID card, and remove the System ID card
from the module being replaced.
6. Install the System ID card in the replacement static switch. Take care when inserting the
card that it is properly aligned with the guide rails in the static switch module, and is fully
seated and secure the retaining screw.
7. Insert the replacement static switch into the UPS enclosure and seat securely to ensure
all connectors are engaged.
8. Install the four screws which secure the module in the enclosure. In order to prevent
alignment problems between the SSW enable switch and the latch, install and tighten
the screw on the upper right hand side of the module first.
9. Enable the module by turning the locking latch clockwise until the arrow points towards
module.
10. Restart the UPS. Verify there are no alarms relating to the static switch following replacement. Return the UPS from external bypass.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
0
1501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

This is how you would replace a SSW.... But why are you replacing it? If its faulty you probably won't be able or shouldn't attempt to transfer to static bypass. This part is hot swap-able and I'd attempt it online if the SSW is reporting faulty.

If you are just replacing it as a scheduled upgrade then your procedure looks fine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:34 AM . Last Modified: ‎2024-03-13 04:10 AM

This is how you would replace a SSW.... But why are you replacing it? If its faulty you probably won't be able or shouldn't attempt to transfer to static bypass. This part is hot swap-able and I'd attempt it online if the SSW is reporting faulty.

If you are just replacing it as a scheduled upgrade then your procedure looks fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore