Symmetra LX 8000 RM alarms and battery identified

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 8000 RM alarms and battery identified
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Jyonano
Crewman Jyonano
Crewman

Posted: ‎2022-08-16 09:28 AM

1 Like
3
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-16 09:28 AM

Symmetra LX 8000 RM alarms and battery identified

I am surprised how difficult it is to  get simple information on these units. 

I have a Symmetra LX 8000 with 2 additional XR modules.  One if the batteries is dead.  C3 01.  It is in the XR 2, but which one?  Which battery is 01?  No chart anywhere on the frame or internet that I can find.  Contacted APC support with our extended warranty,  Useless......   So How do I silence the alarm?  how to do I identify the bad battery.  

The support looked at it and got the raw data and said it was all fine.. But it is not.   The fault light is on and the alarm is going off non stop (WHERE IS THE MUTE!) and the report shows a single bad battery in the XR2.  I have removed 6 of them and they alarm stays one.  Will it turn off right away when I remote the bad one or will it take time to 'notice'?

Any real help would be appreciated. 

 

Jason

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2022-08-17 11:20 PM

0 Likes
2
1753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-17 11:20 PM

Hi Jason

 

Here's a diagram showing the Battery module identification and which Intelligence module monitors them.

If you remove the offending one it should be noticed straight away, if it doesn't I would try a self test.

 

So C3 01 would be the 1st XR frame and the centre module on the 3rd row

 

 

LX Battery Module Identification.png

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2022-08-17 11:20 PM

0 Likes
2
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-17 11:20 PM

Hi Jason

 

Here's a diagram showing the Battery module identification and which Intelligence module monitors them.

If you remove the offending one it should be noticed straight away, if it doesn't I would try a self test.

 

So C3 01 would be the 1st XR frame and the centre module on the 3rd row

 

 

LX Battery Module Identification.png

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jyonano
Crewman Jyonano
Crewman

Posted: ‎2022-08-18 09:36 AM

In response to APC_Matt
0 Likes
1
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-18 09:36 AM

Thank you!  That is the diagram that has eluded me for a year!  I will try this out and let you know how it goes.... 

 

Thanks again. 

 

Jason

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jyonano
Crewman Jyonano
Crewman

Posted: ‎2022-08-23 11:29 AM

In response to Jyonano
0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-23 11:29 AM

That worked perfectly!  I now know what to replace and have silenced the incessant beeping in that building!  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore