Symmetra LX 16000 Number of Betteries Increase/Decrease?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16000 Number of Betteries Increase/Decrease?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

0 Likes
2
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

Symmetra LX 16000 Number of Betteries Increase/Decrease?

I have looked in the forums and haven't found what I have been looking for so I am posting this.

I have had a Symmetra LX 16000 in our server room for about a month now. I have it set up to a syslog server to capture the events and notify me if anything is out of the normal, ie power issues in and out of the Symmetra. Below is the Recent Device Events that have been making me scratch my head lately.

10/04/2011 20:15:55 UPS: The number of batteries increased.
10/04/2011 20:15:39 UPS: The number of batteries decreased.

10/04/2011 08:15:54 UPS: The number of batteries increased.
10/04/2011 08:15:39 UPS: The number of batteries decreased.

I don't know why this is happening becuase there are only two people that have acces to our server room where the symmetra is located, and niether one of us have messed with it since installation.

If anyone has any information on this issue or a way to fix the issue, please let me know and thanks in advance.

~jkbucksot
Honda Power Equipment Mfg, Inc.

Message was edited by: jkbucksot

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

0 Likes
0
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

If you have any external battery cabinets (XR Frames), that would be my first area of focus here. It's possible that you have an XR Comm Card that is on its way out.

A typical Symmetra LX can only hold up to 4 battery modules, so if you have more than that, you likely have at least one XR frame.

(There is a Symmetra LX with an integrated 9-battery XR frame, but that would not be using a traditional XR Comm Card)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

0 Likes
0
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

This usually indicates that one of the batteries isn't seated properly. Of course they can be other causes such as bad batteries, low battery voltage etc but you would likely see other faults/entries in the log. Assuming you do not have any faults and you don't see any other alarms in the log, I would recommend reseating each battery(lift up on the handle, pull towards you and then reinstall). You don't need to slam it in but give it a little bit of force. If this doesn't work, I would recommend calling tech support at 800-800-4272 and they will help you determine the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:17 AM . Last Modified: ‎2024-03-13 02:59 AM

If you have any external battery cabinets (XR Frames), that would be my first area of focus here. It's possible that you have an XR Comm Card that is on its way out.

A typical Symmetra LX can only hold up to 4 battery modules, so if you have more than that, you likely have at least one XR frame.

(There is a Symmetra LX with an integrated 9-battery XR frame, but that would not be using a traditional XR Comm Card)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore