Symmetra 80k Total Amps vs. Amps per phase

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra 80k Total Amps vs. Amps per phase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

0 Likes
3
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

Symmetra 80k Total Amps vs. Amps per phase

I have a 200 amp breaker going to my Symmetra 80k. It is 3 phase (idk if they are all 3 phase). Is that 200 amps per phase or 200 amps total across the 3 phases? The UPS is currently showing 216 amps on the display.

Thanks, Chris

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

0 Likes
0
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

200 Amps per phase.

In a previous email you stated that you have a Symmetra PX80 with 60KW of power modules installed. What configuration do you have?

Does the Symmetra have a PDU with a Transformer 480/208? 208/208? or is it transformerless?

The reason I ask is because the recommended breaker size for an 80KW Symmetra 208V is 350A or Symmetra w 480/208 Xfmer PDU is 150A.

I'd guess you have no PDU or 208/208xfmr or PDU no XMFR because you have a 200A breaker which if they only sized for max 60KW of load would be a total of 166A so a 175 or 200A breaker would have been installed.

Saying that if you wanted to ever expand to 80kw you may need to upsize your breaker and conductor size. This is assuming you have the capacity to do so.

I believe you need to get an electrical engineer involved with your expansion to ensure you have the proper feeder and UPS capacity. This forum isn't an ideal arena for advice for this because of the variables involved which an experience engineer needs to be aware of.

Message was edited by: upsguy

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

200 Amps per phase.

In a previous email you stated that you have a Symmetra PX80 with 60KW of power modules installed. What configuration do you have?

Does the Symmetra have a PDU with a Transformer 480/208? 208/208? or is it transformerless?

The reason I ask is because the recommended breaker size for an 80KW Symmetra 208V is 350A or Symmetra w 480/208 Xfmer PDU is 150A.

I'd guess you have no PDU or 208/208xfmr or PDU no XMFR because you have a 200A breaker which if they only sized for max 60KW of load would be a total of 166A so a 175 or 200A breaker would have been installed.

Saying that if you wanted to ever expand to 80kw you may need to upsize your breaker and conductor size. This is assuming you have the capacity to do so.

I believe you need to get an electrical engineer involved with your expansion to ensure you have the proper feeder and UPS capacity. This forum isn't an ideal arena for advice for this because of the variables involved which an experience engineer needs to be aware of.

Message was edited by: upsguy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

0 Likes
0
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:08 AM

symmetra unit with 3phases in and 3 phases out (electrical configuration), should display each amps consumed by load separately on phases l1,l2,l3, you can refer to the product manual on the apc site.
in general unit with 3 phases in and 1 phase out,display the total amps out consumed by the load, to configure the amps consumed by each phase you should divide
total amps out by 3.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

I sent an email if you are interested.

Thanks, Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore