Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Rack Mounted UPS In Series

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Rack Mounted UPS In Series
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
9
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

Rack Mounted UPS In Series

Do you have any information on or heard of rack mounted UPS units in series with the house ups system? A Customer wants to do this in my data center.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

Rack mounting refers to the Computer servers designed for rack-mounting can include a number of extra features to make the server easy to use in the rack:

The sliding rails can lock in various extended positions to prevent the equipment from moving when extended out from the rack for service.
The server itself might have locking pins on the sides that just drop into slots on the extended rail assembly, in a manner similar to a removable kitchen drawer. This permits a very easy server installation and removal since there is no need for the server to be held in midair while someone fastens each rail to the sides of the server with screws.
Some manufacturers of rack-mount hardware include a folding cable tray behind the server, so that the cables are held into a neat and tidy folded channel when inside the rack, but can unfold out into a long strip when pulled out of the rack, allowing the server to continue to be plugged in and operating normally even while fully extended and hanging in midair in front of the rack. This piece of equipment thus simplifies maintenance, but at the cost of providing a restriction to airflow.
Rack-optimized servers might duplicate indicator lights on the front and rear of the rack to help identify a machine needing attention, or provide a separate "identify" LED indicators on both sides of the server (which can be turned on in software or by pushing an associated button). Since some configurations permit over fifty 1U servers in a single rack, this provides a simple method to determine exactly which machine is having a problem when at the rear of the rack.
A handle may be provided at the rear of the server rails, to help pull or push the server without having to pull on the cables.

[cloud services|http://www.qualitytech.com/]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

i have not. what model UPS are you looking at? what are they hoping to achieve with this set up? what type of UPS home system do they have?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

Hi,

House UPS's are Liebert 610s, I found this link this is considered daisy chaining,

http://emea-en.apc.com/app/answers/detail/a_id/397/~/daisy-chaining-ups

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

oh ok, you should not daisy chain UPSs for those reasons. i wasnt sure if they were trying to achieve something else such as monitoring them all or something else, i dont even know what.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

i believe they intend to connect the units in a parallel configuration, either redundant or capacitive installation.
in any case, the liebert 610 can be paralleled by a sync box. APC would not be able to assist with this request, as it is a 3rd party unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

I can't begin to think of a reason you would want to parallel rack mount UPS for either capacity or redundancy.... The hassle and cost couldn't justify any gains of doing this.

Same goes for UPS in series. The only recommended method is with Large UPS systems and that is to feed the Bypass of the Primary UPS with the output of the secondary UPS. This is called ISO Redundant and would accomplish the same basic function. Most small rack mount UPS however do not have the option of dual mains input.

If you really need the redundancy of two UPS I would recommend installing a rackmount transfer switch which can be fed by the House UPS and the Rackmount UPS and in the event either fails the load would still have a UPS source available.

http://www.apc.com/products/family/index.cfm?id=14

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

It is not uncommon to do this, many colocation customers in large data centres install their own UPS which is naturally fed off the site UPS. As long as there is say 5 times size difference between the two it shouldn't cause a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

Adding in components between a protected source and the load only decreases reliability. As parts count goes up you increase single points of failure. The idea of a UPS feed by a UPS may seem like a good idea but a small single phase UPS isn't nearly as reliable as a large 3 phase UPS system and your only introducing a greater risk of failure of doing this.

Just because some people do this in colocation data centers doesn't make it right. A proper colo data center should have a reliability factor multiples higher than a single UPS. If you put a small UPS in series with the protected power path it would negate the entire reason for placing your servers in a colocation data center in the first place.

As stated before if you really want to add an additional UPS for redundancy, use the redundant power supply in the server. If its a single corded device I would use an ATS if you feel your primary UPS is unreliable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:08 AM . Last Modified: ‎2024-03-19 01:07 AM

There are many reasons to be in a colo other than UPS, and while it does introduce another potential failure point there are always stories of major data centres going down when they really shouldn't. At least if a local UPS is used the owner has control over that and can take whatever steps they feel are necessary to maintain uptime such as replacing the whole UPS every 3 years with a new one if they wish.

The OP was asking whether it is possible and Yes it is, the additional failure point is their customer's problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

Rack mounting refers to the Computer servers designed for rack-mounting can include a number of extra features to make the server easy to use in the rack:

The sliding rails can lock in various extended positions to prevent the equipment from moving when extended out from the rack for service.
The server itself might have locking pins on the sides that just drop into slots on the extended rail assembly, in a manner similar to a removable kitchen drawer. This permits a very easy server installation and removal since there is no need for the server to be held in midair while someone fastens each rail to the sides of the server with screws.
Some manufacturers of rack-mount hardware include a folding cable tray behind the server, so that the cables are held into a neat and tidy folded channel when inside the rack, but can unfold out into a long strip when pulled out of the rack, allowing the server to continue to be plugged in and operating normally even while fully extended and hanging in midair in front of the rack. This piece of equipment thus simplifies maintenance, but at the cost of providing a restriction to airflow.
Rack-optimized servers might duplicate indicator lights on the front and rear of the rack to help identify a machine needing attention, or provide a separate "identify" LED indicators on both sides of the server (which can be turned on in software or by pushing an associated button). Since some configurations permit over fifty 1U servers in a single rack, this provides a simple method to determine exactly which machine is having a problem when at the rear of the rack.
A handle may be provided at the rear of the server rails, to help pull or push the server without having to pull on the cables.

[cloud services|http://www.qualitytech.com/]

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore