Symmetra 40K In bypass in response to an overload
We get alerted to these about once a month but I can't see what's triggering it, there isn't much on the UPS. Any idea on what I can do to stop these errors?
|
|||||||||||||||||||||||||||||||||||||||||||
|
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 12:45 AM . Last Modified: 2024-01-31 03:00 AM
Hi,
The event indicates the UPS passed a self-test. That is a good thing. The UPS will run a self-test to verify the batteries can sustain the load.
If you have other concerns or further questions please contact APC by Schneider Electric 3 phase UPS support at 1-800-555-2725 then option 4
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 12:45 AM . Last Modified: 2024-01-31 03:00 AM
Hi,
The event indicates the UPS passed a self-test. That is a good thing. The UPS will run a self-test to verify the batteries can sustain the load.
If you have other concerns or further questions please contact APC by Schneider Electric 3 phase UPS support at 1-800-555-2725 then option 4