Switching Outlets on "stand alone" Smart UPS?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Switching Outlets on "stand alone" Smart UPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:25 AM

0 Likes
5
2581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:25 AM

Switching Outlets on "stand alone" Smart UPS?

Hello,

i have a smart UPS, have configured the outlet-groups, but they don't switch off at all.

 

That UPS has no PowerChute or Network-shutdown -client connected.

Due to location it is only a supply for a Qnap-NAS , telefone router switch and so on.

 

Is it possible to have outlets switched as setup in the display in case of an outage?  (without powerchute connected)

(Smart-UPS SMT-1000iC)

thx.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • outlet
  • PowerChute
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

0 Likes
0
2580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

Hi Bill,

The Load shedding was exactly my problem.

Once checked and set up, things are working as planned.

Thank you very very much.

Earlier I called support on this matter, and they could not help...

"please install original software, without software it don't work"   ๐Ÿ˜ž

 

So now i am glad to have the solution.

 

Thx,

and have a nice evening.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:25 AM

0 Likes
0
2580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:25 AM

Hi,

On 1/1/2021 9:25 AM, Detlef said:

Is it possible to have outlets switched as setup in the display in case of an outage? 

Yes. From the LCD panel go to Configuration, and set to Advanced. The from within the Advanced Configuration menu using the up or down arrow and scroll to Main Outlet Group, load Shedding. Enable load shedding then configure either time on battery or runtime remaining. If you configure time on battery the UPS will run on battery for x time then power off. If you configure runtime remaining the UPS will run on battery until the runtime falls below x and then power off. You can also set an individual shutdown time for Outlet Group 1. 

See pages 19 and 20 of the attached user's guide. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

0 Likes
0
2580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

Hello Bill,

i have read the manual carefully, but wasn't able to find the problem.

Attached you can find a combined screenshot of my setup. (Viewed with nmc)

In case of outage nothing switches off or on (after) within the timings.

 

I need the timings basically for switching off  and switching on with delay!

I want to have a delay at least 30 seconds (Main) and 60 seconds (Group 1) to be sure ,

that power is stable on again. (Maybe even longer)

Thx

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

0 Likes
0
2580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

Hi,

You needed to configure the load shedding settings to trigger the shutdown. Once shutdown has occurred when AC is restored the power on delay will be honored. 

Example: click on the load shedding power fail lasts longer than. Then set the delay to 600 seconds. When the UPS has been running on battery for 10 minute the shutdown process will start. 

 

NOTE: The 600 second power off delay for the main group will not begin until the 360 second delay has completed for group one. So, the actual power off delay for the main is 16 minutes. 

LxY1boBQ3mmgbkDUFaTvSw%3D%3D.pngLxY1boBQ3mmgbkDUFaTvSw%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

0 Likes
0
2580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

Hi Bill,

 

ok, i will try right away. Come back to you shortly.

 

 

thx

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

0 Likes
0
2581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:12 AM . Last Modified: โ€Ž2024-03-08 01:24 AM

Hi Bill,

The Load shedding was exactly my problem.

Once checked and set up, things are working as planned.

Thank you very very much.

Earlier I called support on this matter, and they could not help...

"please install original software, without software it don't work"   ๐Ÿ˜ž

 

So now i am glad to have the solution.

 

Thx,

and have a nice evening.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore