Windows Server 2012 R2 installed PowerChute BE (10.0.1, 9.5) has 2 UPS connected (Smart-UPS RT 1000 COM and Smart-UPS 2200 USB), but only one is detected. If two are connected, then Smart-UPS RT 1000 COM is detected (during agent installation), but Smart-UPS 2200 USB is not.. If disable Smart-UPS RT 1000 COM, then Smart-UPS 2200 USB is detected in agent. Is it possible to see two UPS in the agent?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:12 AM . Last Modified: 2024-03-08 01:25 AM
Hello,
The PowerChute Agent is designed to communicate with a single UPS. If you would like to communicate with redundant UPS you will need to uninstall the PowerChute Agent, install a network card in each UPS, then install PowerChute Network Shutdown configured for redundant UPS. See Schneider Electric Application Note 98 "Using PowerChute Network Shutdown in a Redundant-UPS Configuration".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:12 AM . Last Modified: 2024-03-08 01:25 AM
Hello,
The PowerChute Agent is designed to communicate with a single UPS. If you would like to communicate with redundant UPS you will need to uninstall the PowerChute Agent, install a network card in each UPS, then install PowerChute Network Shutdown configured for redundant UPS. See Schneider Electric Application Note 98 "Using PowerChute Network Shutdown in a Redundant-UPS Configuration".
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of