Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:11 AM . Last Modified: 2024-03-08 01:25 AM
Windows Server 2012 R2 installed PowerChute BE (10.0.1, 9.5) has 2 UPS connected (Smart-UPS RT 1000 COM and Smart-UPS 2200 USB), but only one is detected. If two are connected, then Smart-UPS RT 1000 COM is detected (during agent installation), but Smart-UPS 2200 USB is not.. If disable Smart-UPS RT 1000 COM, then Smart-UPS 2200 USB is detected in agent. Is it possible to see two UPS in the agent?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:12 AM . Last Modified: 2024-03-08 01:25 AM
Hello,
The PowerChute Agent is designed to communicate with a single UPS. If you would like to communicate with redundant UPS you will need to uninstall the PowerChute Agent, install a network card in each UPS, then install PowerChute Network Shutdown configured for redundant UPS. See Schneider Electric Application Note 98 "Using PowerChute Network Shutdown in a Redundant-UPS Configuration".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:12 AM . Last Modified: 2024-03-08 01:25 AM
Hello,
The PowerChute Agent is designed to communicate with a single UPS. If you would like to communicate with redundant UPS you will need to uninstall the PowerChute Agent, install a network card in each UPS, then install PowerChute Network Shutdown configured for redundant UPS. See Schneider Electric Application Note 98 "Using PowerChute Network Shutdown in a Redundant-UPS Configuration".
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.