Switched PDU Notification Settings

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Switched PDU Notification Settings
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:28 PM

0 Likes
1
1010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:28 PM

Switched PDU Notification Settings

I have an installed base of 176 AP7901 & AP7911 PDUs in my datacenter. I have written a script to do most of the management of these devices including uploading and downloading a common config.ini. There are some config options that show in the web interface but are not in in the config file, namely the notification settings. I would like to share common notification settings between all the devices. As it looks right now, I would have to "touch" every device and make the changes. This is very annoying to do.

Are there any programs out there that can upload the notification configs to all the PDUs without having to login to each one and change them? I am interested in turning off some alerts and changing the notification delays, repeats and times that a notification is sent to the SNMP server.

Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:27 PM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:27 PM

the notification settings are in the config.ini. they are at the bottom of the file where you see all of the events that can occur.

there is no easy way to configure notifications globally for different PDUs other than configuring it on one through the web interface and copying it over to different PDUs via the way you already are.

on my environmental monitoring unit, I have it set for:

When the event condition persists for 5 seconds, an E-mail will be sent to:
apc@apc.com
The e-mail will be repeated every 3 minutes, up to 4 times.

in the config.ini, this translates to:

; RS: Low temperature threshold violation.
E1907=ES,E(++05S+03M04:::),T (:::::)

the ()'s should be ] and ['s but the forum code changes them.



I know that E is for email, T is for traps (SNMP settings) but i am not sure of the exact syntax so I dont recommend setting it through the config.ini file manually. i'd recommend setting that part through the web interface then uploading it after. you can just upload the (EventActionConfig) part of the config.ini after you are done and it will just append it to the current config.ini - no need to upload the entire config.ini again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:27 PM

0 Likes
0
1010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:16 AM . Last Modified: ‎2024-02-14 10:27 PM

the notification settings are in the config.ini. they are at the bottom of the file where you see all of the events that can occur.

there is no easy way to configure notifications globally for different PDUs other than configuring it on one through the web interface and copying it over to different PDUs via the way you already are.

on my environmental monitoring unit, I have it set for:

When the event condition persists for 5 seconds, an E-mail will be sent to:
apc@apc.com
The e-mail will be repeated every 3 minutes, up to 4 times.

in the config.ini, this translates to:

; RS: Low temperature threshold violation.
E1907=ES,E(++05S+03M04:::),T (:::::)

the ()'s should be ] and ['s but the forum code changes them.



I know that E is for email, T is for traps (SNMP settings) but i am not sure of the exact syntax so I dont recommend setting it through the config.ini file manually. i'd recommend setting that part through the web interface then uploading it after. you can just upload the (EventActionConfig) part of the config.ini after you are done and it will just append it to the current config.ini - no need to upload the entire config.ini again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of