Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
APC PDU requried
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2803:16 AM. Last Modified: 2024-02-1410:27 PM
APC PDU requried
Hi Dear,
I purchased a AP7930 for our 60th Hudson Co-location. Now I have a need for a PDU for our one Wilshire Co-location.
Here the power source is different.
The supply is 230 v with stand input plug. We have 10 AMP current now.
I need your help to find out the exact model of PDU required.
Feature wise I am looking for 16-24 plug sockets.
Browser access to power down and Up each Sockets.
From browser see each socket power consumption.
Notify us if we use more than 10 AMP current.
We need to use Dell Power Edge 1850 & 1950 servers.
These Switched Rack PDUs allow you to control the outlets (on/off, set outlet groups, etc.) via a browser, and view current draw via a browser as you requested.
We also have an AP7850 (Zero U, 10A, 230V, (16) C13 outlets) option for the 230V input range but this is a metered PDU, and does not have the outlet control options that the Switched Rack PDUs offer. It will however, let you access the PDU via a browser to view current draw.
I have tried double checking to see if these PDUs are compatible with the Dell Poweredge 1850/1950 servers, and have been unable to find the exact plug type used by the servers. I know the larger 28xx PowerEdge's can use C20 connections...but you may have to check with Dell to confirm the spec on the 1850/1950.
These Switched Rack PDUs allow you to control the outlets (on/off, set outlet groups, etc.) via a browser, and view current draw via a browser as you requested.
We also have an AP7850 (Zero U, 10A, 230V, (16) C13 outlets) option for the 230V input range but this is a metered PDU, and does not have the outlet control options that the Switched Rack PDUs offer. It will however, let you access the PDU via a browser to view current draw.
I have tried double checking to see if these PDUs are compatible with the Dell Poweredge 1850/1950 servers, and have been unable to find the exact plug type used by the servers. I know the larger 28xx PowerEdge's can use C20 connections...but you may have to check with Dell to confirm the spec on the 1850/1950.