Surt D5000xl error codes

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Surt D5000xl error codes
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

0 Likes
2
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

Surt D5000xl error codes

Hi, I am in the process of repairing a mainboard for a SURTD5000XL UPS. The unit was initially dead. after replacing a faulty PWM and transistor and with new batteries I manage to get the beast to turn on. I now see some sort of error code on the LED display. Bypass LED + Fault LED + center LED (on batt charge bar). Is this a loading problem as I only have a monitor connected or a configuration problem or is my mainboard still faulty.I have tried some combinations on the buttons and manage to get the "online" led with "batt charge barr leds" on for about a secound before it changes back to the state metioned first.

a service manual or LED error code table would be very helpfull.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

0 Likes
0
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

Thanks, after your suggestion I went back to troubleshooting and found another transistor that breaks through as the unit start up, it was replaced today.

I am now able to turn the UPS on when not connected to mains and it runs purely off the batts. When I connect the mains the no-load condition led comes up "X" as well as the "bypass led". Bypass is not selected in front the slide switch is set to "online" By playing with the buttons I can get the unit to show online "~" with batt leds on but after 10 seconds it returns to the no load and bypass state with a short beebping sound.

I suspect now something on the primary side that is not connected, mains fuse or cable etc.

I am worried that I am loading it to lightly and that my input cannot provide enough current through the wires as I am using standard kettle cord to test, which is highly under rated for this model.

Have attached pics of online (running of batts no input supply) as well as when I have mains connected.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

0 Likes
0
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

is the UPS unloaded at this point? this generally requires a replacement but we don't do repair on them so i don't know what the cause is. the problem is indicated as PFC Failure and could be caused by many different things. it appears to relate to negative and positive DC busses having an issue with their voltage being out of range.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

0 Likes
0
1505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:25 AM . Last Modified: ‎2024-03-10 11:24 PM

Thanks, after your suggestion I went back to troubleshooting and found another transistor that breaks through as the unit start up, it was replaced today.

I am now able to turn the UPS on when not connected to mains and it runs purely off the batts. When I connect the mains the no-load condition led comes up "X" as well as the "bypass led". Bypass is not selected in front the slide switch is set to "online" By playing with the buttons I can get the unit to show online "~" with batt leds on but after 10 seconds it returns to the no load and bypass state with a short beebping sound.

I suspect now something on the primary side that is not connected, mains fuse or cable etc.

I am worried that I am loading it to lightly and that my input cannot provide enough current through the wires as I am using standard kettle cord to test, which is highly under rated for this model.

Have attached pics of online (running of batts no input supply) as well as when I have mains connected.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of