APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
Is the Static Switch Module (SSW) on a PX 40kVA hot swapp??
Symmetra PX 40kW Scalable to 40kW N+1, 208V
PX 40kVA model: SYCF40KF or SY40K40F
SSW model: SYSW40KF
the Static Swich module can be pull out without drop the load?
is hot swappable?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
In terms of the loads (servers ) staying up and NOT having to be shut down, it is swappable. I'd recommend getting an APC Field Service Engineer in to do this as it is not obvious how to do it to the end user, nor well documented. Good luck !
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
it is NOT hot swappable - you need to shutdown the UPS and in full maintenance bypass.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
you are right it´s not hotswappable....
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:57 AM . Last Modified: 2024-03-13 01:10 AM
In terms of the loads (servers ) staying up and NOT having to be shut down, it is swappable. I'd recommend getting an APC Field Service Engineer in to do this as it is not obvious how to do it to the end user, nor well documented. Good luck !
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.