Staggered Network Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Staggered Network Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
conker_apc
Ensign conker_apc
Ensign

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
6
1533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Staggered Network Shutdown

I've got a Smart UPS 2200 XL Rackmount unit with a network management card (AP9617) and I was wondering how to configure the shutdown procedures.
I've connected all but one of the machine to the network management card with PCNS.

I would like to have all of the machines except 1 shut down at x minutes remaining.
I would then like to have the remaining machine shutdown.

If I could set the first group to shutdown at 10 minutes left, and the final machine to shutdown at 5 minutes left, that would be great.

The reason for this is that we have virtual servers. We'd like to shutdown the virtual servers, and then shut down the physical server they are hosted on.
The physical server is a Linux box, and the virtual servers are all windows 2003 instances.

My current plan is to connect the Linux box directly to the UPS via the USB or serial cable, and then use the regular version of PowerChute to shutdown at 5 minutes remaining or whatever I can configure.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
conker_apc
Ensign conker_apc
Ensign

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Awesome.
We've currently got 1 network card and 1 environment sensor card.
We're going to (for now) use the environment sensor UPS with a virtual instance running powerchute (not the network client).
It'll be able to give us notifications on the temperature, and we don't care if it shuts down gracefully (it's just a virtual instance we don't use much).

Is there any way to pipe the environment sensor data from the one UPS to the other, without buying the $190 upgrade kit, or the $500 network + environment card?

Will be doing some tests next week and I'll post back here.

Message was edited by: conker

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

If you bought a SmartSlot expansion chaissis and somehow found someone who has a Measure-UPS device, you should be able to integrate them with the NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

conker_apc
Ensign conker_apc
Ensign

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Now I'm even more confused.

How do I configure a single network connected server to gracefully shutdown when the UPS goes into low battery mode?
How do I define what low battery mode is?

I have the management card installed and set up.
I have PCNS installed on the server I want to shut down gracefully.
I have that server registered as a client on the network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

You're on the right track:

Essentially you have two ways to shutdown your servers based on battery life:
1. Low battery duration (configured on the NMC under UPS>Configuration>Shutdown). By default, all PCNS clients will begin their shutdown when this estimated runtime is reached. This is also when the UPS will beep rapidly, warning of a low battery condition.
2. PCNS configured shutdown event (there are many). This is in the PCNS interface. The one you are interested in is "On Battery". You can configure the time the PCNS client "waits" after the UPS switches to battery, then shuts down.

Here's Simple Example:
Server 1 - Highly critical
Server 2 - Somewhat Important
Server 3 - Non-critical

Assuming your UPS has 20 mins of runtime and the low battery duration is set to 5 mins:
PCNS on server 3 - on battery shutdown after 60 seconds
PCNS on server 2 - on battery shutdown after 600 seconds (10 mins, PCNS setting is in seconds)
PCNS on server 1 - left to default

Here's what your timeline would look like:
12:00 Power goes out
12:01 Server 3 shuts down
12:10 Server 2 shuts down
UPS will then run until it estimates 5 mins LEFT of battery, which is when server 1 will shutdown.

The advantage is that you can bring down non-critical servers early, which will INCREASE the runtime of the UPS (less load) for your critical equipment. So in our example, server 1 wouldn't shutdown at 12:15 but probably somewhere near 12:25-40 (depending on the size of the UPS), since the UPS would have less load from shedding the non-critical servers and gaining runtime.

I hope this helps.

Message was edited by: Cap1

Reply

Link copied. Please paste this link to share this article on your social media post.

conker_apc
Ensign conker_apc
Ensign

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Thanks for clearing that up. I didn't realize there were options to set in the events page other than a simple check mark.

Cap1 wrote:
Low battery duration. By default, all PCNS clients will begin their shutdown when this estimated runtime is reached. This is also when the UPS will beep rapidly, warning of a low battery condition.
The manual states that the "low-battery duration" setting in the NMC config is "How long the UPS can run on battery power after a low-battery condition occurs." This is poorly worded. I initially took this to mean "How long, *after reaching a low-battery condition*, the UPS will run before shutting down.", which makes sense, when you consider that you are directly changing this setting.
The way it is worded now makes it seem like you are altering how long the UPS can run on battery power, after a low-battery condition occurs. I guess you are, but only indirectly, by altering the definition for a low-battery condition. The word "after" implies that the low-battery condition occurs first, then your setting is applied, as a rule.

1: Does this mean that after a low-battery condition occurs, the UPS will run for x minutes, and then shutdown all servers? If so, how do I specify the conditions for a low-battery? Is this configurable (x minutes of runtime), or is it a fixed setting in the UPS?
--Nevermind - I figured this out above by going over their poorly worded definition.

2: If I want a server to be up as long as possible, how do I set up it's shutdown event? Do I set it to shutdown at 0 seconds? Some large number of seconds? Or do I NOT set the event at all (and the NMC shuts down all clients when the low-battery condition occurs, which is different from the on battery condition)?
--Rereading your post, I see it's the last option I listed (not setting up the event at all).

Thanks a bunch. Now I've just got to figure out the whole redundant power supplies on a separate, identical UPS.

Message was edited by: conker

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

I noticed the end of your post stating that you have redundant power supplies on a different UPS. The simplest configuration for that is to get another Network Management Card, install it within that second UPS, and reinstall PowerChute Network Shutdown as a Custom Install. That will let you register each machine with BOTH management card IP's. The way the shutdown will work is that if there is a configured shutdown after X minutes on battery, the PCNS client will ignore the first On Battery message from UPS A. When UPS B switches to battery (if A remains on), it will then begin its timer for graceful shutdown. That will allow you to have your machines up and running off of utility power in the event that UPS A, on a different circuit, or UPS B, on a different circuit, fails over.

Reply

Link copied. Please paste this link to share this article on your social media post.

conker_apc
Ensign conker_apc
Ensign

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

0 Likes
0
1533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:21 AM

Awesome.
We've currently got 1 network card and 1 environment sensor card.
We're going to (for now) use the environment sensor UPS with a virtual instance running powerchute (not the network client).
It'll be able to give us notifications on the temperature, and we don't care if it shuts down gracefully (it's just a virtual instance we don't use much).

Is there any way to pipe the environment sensor data from the one UPS to the other, without buying the $190 upgrade kit, or the $500 network + environment card?

Will be doing some tests next week and I'll post back here.

Message was edited by: conker

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of