Stack overrun. Task 31.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Stack overrun. Task 31.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
4
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

Stack overrun. Task 31.

Hello everyone,
We installed our new Symmetra PX this week end and we had an alarm.

21.07.2009 02:16:42 System: Set Date or Time.
21.07.2009 01:15:41 System: Set Date or Time.
21.07.2009 00:14:41 System: Set Date or Time.
20.07.2009 23:14:42 System: Set Date or Time.
20.07.2009 22:16:08 UPS: Restored the local network management interface-to-UPS communication.
20.07.2009 22:15:45 System: Network service started. System IP is 172.27.16.222 from manually configured settings.
20.07.2009 22:15:45 System: Warmstart.
20.07.2009 22:15:24 System: Restarting. Stack overrun - Task 31.Stack overrun.
20.07.2009 22:14:33 System: Set Date or Time.
20.07.2009 21:14:33 System: Set Date or Time.
20.07.2009 20:14:33 System: Set Date or Time.
20.07.2009 19:14:33 System: Set Date or Time.
20.07.2009 18:13:33 System: Set Date or Time.

Where can it comes from?
Can this be a problem with the updating of the date and time synchronised with our NTP server?

We also use SNMPv1 for Acess.

thanks for your help!!
Sam

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 04:27 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:27 AM . Last Modified: ‎2024-03-19 01:30 AM

You're running version 3.3.1 of the Symmetra 3-Phase application. The latest is v3.5.8 which you can get here. We'll see if that solves the problem and take things from there.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

Hello everyone,
We installed our new Symmetra PX this week end and we had an alarm.

21.07.2009 02:16:42 System: Set Date or Time.
21.07.2009 01:15:41 System: Set Date or Time.
21.07.2009 00:14:41 System: Set Date or Time.
20.07.2009 23:14:42 System: Set Date or Time.
20.07.2009 22:16:08 UPS: Restored the local network management interface-to-UPS communication.
20.07.2009 22:15:45 System: Network service started. System IP is 172.27.16.222 from manually configured settings.
20.07.2009 22:15:45 System: Warmstart.
20.07.2009 22:15:24 System: Restarting. Stack overrun - Task 31.Stack overrun.
20.07.2009 22:14:33 System: Set Date or Time.
20.07.2009 21:14:33 System: Set Date or Time.
20.07.2009 20:14:33 System: Set Date or Time.
20.07.2009 19:14:33 System: Set Date or Time.
20.07.2009 18:13:33 System: Set Date or Time.

Where can it comes from?
Can this be a problem with the updating of the date and time synchronised with our NTP server?

We also use SNMPv1 for Acess.

thanks for your help!!
Sam

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

Hi Sam,

>
Can this be a problem with the updating of the date and time synchronised with our NTP server?
>

Most likely; task 31 on your system handles NTP.

To help us look into this issue, could you find out what application is loaded on the network management card? This is shown on the top of the telnet banner, for instance:

American Power Conversion               Network Management Card AOS      v3.6.1
(c) Copyright 2008 All Rights Reserved  ISX-RDP                          v3.5.7
or on the Web interface under administration->general->about

If it's an older version of the NMC application, we can try upgrading to the latest version and seeing if the problem persists.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:26 AM . Last Modified: ‎2024-03-19 01:30 AM

Hello voidstar,
Thanks for your answer.
Here's what I found under Administration->General->About
Hardware Factory

Model Number: AP9617
Serial Number: ZA0635003905
Hardware Revision: A10
Manufacture Date: 08/22/2006
MAC Address: 00 C0 B7 81 96 42
Management Uptime: 2 Days 9 Hours 41 Minutes



Application Module

Name: sy3p
Version: v3.3.1
Date: 01/05/2007
Time: 16:33:45



APC OS (AOS)

Name: aos
Version: v3.3.4
Date: 01/05/2007
Time: 14:23:44

hope this can help!
Samy

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 04:27 AM . Last Modified: ‎2024-03-19 01:30 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:27 AM . Last Modified: ‎2024-03-19 01:30 AM

You're running version 3.3.1 of the Symmetra 3-Phase application. The latest is v3.5.8 which you can get here. We'll see if that solves the problem and take things from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of