Some hosts losing power during utility failure, others do not.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Some hosts losing power during utility failure, others do not.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
3
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Some hosts losing power during utility failure, others do not.

Hello Forum,

I have a few servers on a SmartUPS with an AP9630 mgmt card in it.

Mgmt card is at: App (v6.4.6), AOS (v6.4.6), Boot Monitor (v1.0.8).

UPS Firmware: 691.16.D

Extended battery pack on this unit.

Unit "new to us" 2016 - New batteries then.

Expanded battery pack new in 2013 - so those batteries are getting fairly old.

On this UPS we have 4-5 HP DL380 Gx boxes + KVM rack console and an HP V1910 24 port switch.

Load shows 3 of 5 lights

Batts show 5 lights

Last night two of the HP boxes, both running VMware, appear to have power cut.

The other boxes on the UPS did not.

When we arrived the amber power buttons were glowing on those servers but the others were running fine and never rebooted.

These servers have dual power supplies plugged in on different banks of plugs on the UPS (ie. different UPS circuit breakers).

Utility power dropped for 2 seconds during this incident.

I don't have the APC tools on the hosts in question but none of the other servers in that rack had an issue.

What should I look at first? Just swap the external expansion pack batteries out with new ones?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

This technote explains the difference :

http://www.apc.com/us/en/faqs/FA156514/

I'd keep an eye on the PSUs in those servers though. Low is still supposed to be ~10ms an pretty much anything should ride that out if it's in good nick.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Not immediately helpful, but I had a similar issue with servers on an SUA3000 late last year. After lots of diagnostics it turned out the power supplies in the units that rebooted were old enough to have degraded such that their full-load hold up time was on the border of the UPS worst case switch-over time.

So if the mains failure happened at the wrong time in the mains cycle, the UPS didn't pick up the failure fast enough to stop the server PSU from dropping the power good signal. After a *lot* of manual testing, it turned out it was happening about 30% of the time based on where in the mains cycle the power was interrupted. New power supplies in the server fixed that and we haven't seen an issue since.

In my case the power supplies were some 8 years old and the rated hold up time of >20ms had fallen down to ~8ms when fully loaded.

The other thing worth looking at is the "sensitivity" setting on the UPS. Setting it to high will make the UPS faster in detecting a mains loss. If you have noisy mains, it may also mean it switches to battery more often, so there's always a tradeoff.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Thank you for the pointers. I think you may have something with the sensitivity. The other two racks in that room have it set to high, the problem one set to low.

We are going to change it to high as well and monitor.

We don't seem to have the other two switching the battery often so we must be fed fairly clean power.

THank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

This technote explains the difference :

http://www.apc.com/us/en/faqs/FA156514/

I'd keep an eye on the PSUs in those servers though. Low is still supposed to be ~10ms an pretty much anything should ride that out if it's in good nick.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of