Min Return Runtime not having effect

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Min Return Runtime not having effect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Bartolo
Ensign Bartolo
Ensign

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

0 Likes
4
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

Min Return Runtime not having effect

Min Return Runtime not having effect
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

Hi,

Sorry for the inconvenience. If the load is less than 4.5 amps at the time of shutdown the available runtime will not calculated properly and the UPS will power on when AC is restored immediately as you are seeing. To allow the UPS to charge enough to provide the proper protection add an additional delay. Enter a figure into Power On Delay the allow the batteries to be charged before AC is restored to the outlet group/s. 

Another option is to have the load shutdown prior to required runtime of 14 minutes. That way when the UPS restores AC there will be enough runtime to sustain the load. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

0 Likes
0
1789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:34 AM

Hi,

Sorry for the inconvenience. If the load is less than 4.5 amps at the time of shutdown the available runtime will not calculated properly and the UPS will power on when AC is restored immediately as you are seeing. To allow the UPS to charge enough to provide the proper protection add an additional delay. Enter a figure into Power On Delay the allow the batteries to be charged before AC is restored to the outlet group/s. 

Another option is to have the load shutdown prior to required runtime of 14 minutes. That way when the UPS restores AC there will be enough runtime to sustain the load. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bartolo
Ensign Bartolo
Ensign

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Thank you, that explains it. I'll add Power On Delay or increase Low Battery Duration to leave more capacity.

How much charge time would it require to add 15 minutes of runtime for around 500-600 W load?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Hi,

That is tough to say because the charge time is based on the age of the batteries and the environment. I would add a 20 minute delay and adjust after testing. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bartolo
Ensign Bartolo
Ensign

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:17 AM . Last Modified: ‎2024-03-18 02:33 AM

Thanks, I'll do both earlier shutdown and add some charging time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore