Hello
I have a question about condenser of cooling systems .
What's the best solution to implement in a data center which located in 1200 meter above sea level,and consider the maximum temp of the city is 50 degree of Centigrade.
I use ACRD602P and want to know that which condenser part number or model is usable and operational with the part number that i wrote??!!
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM
That's an informative document,and i found my desire type of condenser which is applicable and usable with my environment requirements.
Thanks for your quick reply
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM
Hello. Our normal condensers only go up to 46 degrees C for the out door ambient temperature. Please call into your local sales team and they can work with our configuration team to see if they have a special option condenser that will meet the height and temperature requirements.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM
Hello
You meant that the temperature of condenser is reaches up to 46 degrees C when it works at its maximum load?
sure i would keep in touch with the sales team.
Thank you
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM
Hello. I have attached the tech data manual which has the temperatures at sea level the condensers will work at. The information is on page 46. The 230v 1ph 50hz condensers will work at 40 C, see the note below the table.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM
That's an informative document,and i found my desire type of condenser which is applicable and usable with my environment requirements.
Thanks for your quick reply
Regards