InRow RP DX: Compressor drive fault exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • InRow RP DX: Compressor drive fault exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

1 Like
9
6682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

InRow RP DX: Compressor drive fault exists

Hello,

I'm Rami from Palestine, we are working in a new DC, and installed two Units of ACRP102 InRow RP DX for this DC, when I try to start up the unit for the first time, the unit gave me one alarm and one warning.

  • InRow RP: Compressor drive fault exists
  • High suction pressure alarm exists

Really I can't solve this problem, what are you advise to do?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acrp102
  • alarm
  • compressor
  • drive
  • dx
  • exists
  • fault
  • inrow
  • pressure
  • rp
  • suction
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Dear Sir,

I did that before by myself, but I'm still wait Schneider response.

here my last E-mail to them

Because of the problem occurred by the VFD (Compressor drive), I have checked the history alarms of the VFD, the alarms were:

200000

100000

80000

 

 

Backing to Danfuss Operating Instructions VLT® CDS 302 and CDS 303, these alarms related to Motor output phases loss

 

Alarm 30, 31, and 32.

 

 

 

But I checked the cables which are between the Compressor and the VFD, all of them are OK, and I have checked the Resistance between the Compressor terminals, they were about 1 ohm. Also I checked the starting current of every phase when the VFD trying to run the compressor; the currents were: 16A, 19A and 21A.

 

Now please confirm If I can do these test:

  • Connect the Compressor directly to mains three phases 400Vl-l 50Hz, and check if it run Ok.
  • Swap the VFD between the running ACRP102 to the faulted one.

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Hello. You can swap the VFD's and see if the issue follows the VFD. I would NOT recommend hooking the compressor directly to power. Check the lines to ground at the compressor lugs to make sure the compressor is not grounded.

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Hello

Iw this problem at start up or after an maintenance done?

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Hello Rami. If you can look under the compressor status on the front screen there is a section that shows and alarm code for the compressor drive. If you can get this an call into your local tech support, they will be able to decode it and give you steps on what needs to be done. So common things that you can check in the mean time is to make sure there are no loose wires or connections (will need to be done by an HVAC tech) and make sure the oil sight glass is half to 3/4 full.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Dear Sir,

I did that before by myself, but I'm still wait Schneider response.

here my last E-mail to them

Because of the problem occurred by the VFD (Compressor drive), I have checked the history alarms of the VFD, the alarms were:

200000

100000

80000

 

 

Backing to Danfuss Operating Instructions VLT® CDS 302 and CDS 303, these alarms related to Motor output phases loss

 

Alarm 30, 31, and 32.

 

 

 

But I checked the cables which are between the Compressor and the VFD, all of them are OK, and I have checked the Resistance between the Compressor terminals, they were about 1 ohm. Also I checked the starting current of every phase when the VFD trying to run the compressor; the currents were: 16A, 19A and 21A.

 

Now please confirm If I can do these test:

  • Connect the Compressor directly to mains three phases 400Vl-l 50Hz, and check if it run Ok.
  • Swap the VFD between the running ACRP102 to the faulted one.

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Hello. You can swap the VFD's and see if the issue follows the VFD. I would NOT recommend hooking the compressor directly to power. Check the lines to ground at the compressor lugs to make sure the compressor is not grounded.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Thank you very much

I have changed the VFD and the Compressors 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

yo tuve el mismo problema 

y se soluciono solo cambiando el compresor ya que la logistica fue la culpable de la falla

al abrir el compresor para saber realmente cual era la falla nos dimos cuenta que la alta presion que deberia ir hacia el condensador este botaba todo hacia el mismo compresor dando la alarma de alta presion.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

0 Likes
0
6679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:42 PM

Hello

Iw this problem at start up or after an maintenance done?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

The high pressure in suction usually occurs because the condenser is dirty and does not make the adequate thermal change and is still returning in the form of gas
start by checking the state of the capacitor
check that the fans are working properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
6679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

Hello

It was working fine since 3 years, suddenly showing this alarm. High Suctiob PresPress.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
6679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:04 AM . Last Modified: ‎2024-03-18 11:41 PM

even more so, it must require maintenance to the external unit

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore