SmartUps 3000 drops load for 1sec at power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUps 3000 drops load for 1sec at power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
3
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

SmartUps 3000 drops load for 1sec at power failure

Hi Folks,

I have a fairly old UPS; Model SU3000R3IBX135k, build year 1999.

Been working well for a long time, but recently started dropping load briefly every few weeks. Batteries were about 4 years old so I got a new set in hopes that would keep it going for a bit longer.

New batteries installed; Powerchute says they're ok and at 100%.

Load at 21%.

Did a failure test by switching off the power outlet. All equipment attached to the UPS immediately turned off, and about half to one second later powered back up. From this point the UPS seemed to have no trouble running everything on batteries. Restoring power a few minutes later behaved as expected.

Questions:

1) Are there components in the UPS that commonly fail on old units which would cause such a delay in power failure detection and cut-over to batteries?

2) I also have an APC automatic transfer switch in the mix wired as follows; any chance this would cause a delay in the UPS switching to batteries on legitimate power failure?

Supply ------ [UPS] ----- {ATS} Load

Supply----------------------- {ATS} Load

Same supply - split with a double adapter. 2 inputs into one ATS; straight from outlet, and from UPS. Equipment connected to ATS output.

Rationale was if the UPS had a freakout and dropped load, or needed offline maintenance the ATS would cut to straight wall power and things continue running.

I'm concerned I may have shot myself in the foot with this; Perhaps the ATS detects failure on primary source (UPS), switches to backup - which is also gone since it is the same supply, and then switches back to UPS which is now on batteries, but with all the switching around time the gear has now dropped.

Does that seem plausible?

Cheers,

-Martin.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

What model of ATS do you have? Does either device have any log files during these drops we can review?

You're right on the ATS - this is not a recommended set up and sort of defeats the purpose of an ATS because you are ultimately using the same input power source/circuit. The ATS ideally should be connected to two separate UPSs on two separate power circuits.

Either way, I think we should take the ATS out of the mix somehow because you need to determine if this is a problem with the ATS or the UPS. Maybe switch the preferred power source of the ATS to JUST the supply source with no UPS and repeat the test to see what happens?

What you suspect is definitely feasible with thrashing between sources somehow. My advise though is to at least start by testing JUST with ATS and just with UPS to narrow it down. It could be a problem with an output relay or other UPS or ATS component but I can't tell for sure with what we have so far.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
0
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

What model of ATS do you have? Does either device have any log files during these drops we can review?

You're right on the ATS - this is not a recommended set up and sort of defeats the purpose of an ATS because you are ultimately using the same input power source/circuit. The ATS ideally should be connected to two separate UPSs on two separate power circuits.

Either way, I think we should take the ATS out of the mix somehow because you need to determine if this is a problem with the ATS or the UPS. Maybe switch the preferred power source of the ATS to JUST the supply source with no UPS and repeat the test to see what happens?

What you suspect is definitely feasible with thrashing between sources somehow. My advise though is to at least start by testing JUST with ATS and just with UPS to narrow it down. It could be a problem with an output relay or other UPS or ATS component but I can't tell for sure with what we have so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

Hi Angela,

Thanks for your response & advice. The ATS is a simple old apc one; SU044-1.

I went ahead and took the ATS completely out of the picture by hooking the load directly to the UPS and things work well again, so I was clearly doing something dumb with having that in there fed by the same supply. Looks like they get confused and step on each other in that setup.

Potentially the ATS sensitivity could be tuned to survive this scenario, but considering I don't have a 2nd independent supply anyway I think I'll just simplify things and keep it out.

Cheers,

-M.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:52 PM . Last Modified: ‎2024-03-11 04:25 AM

Thanks for the update. And yes, SU044-1 is quite old. Glad we narrowed it down though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of