SmartUps 1500 LCD Not Showing Events

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUps 1500 LCD Not Showing Events
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
4
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

SmartUps 1500 LCD Not Showing Events

have a SU1500 which would not show any events (actually did show 2 from 2 months ago)

but hasn't shown anything since then such as undervoltages (when lights in office dim)

or power outages (when i pulled the plug). Reset the sampling interval from 2 hours to 1

minute (per APC support) and it, at least, showed an event when I pulled the plug after

the change. i do not understand why changing the sampling interval would affect the event

log. Any thoughts?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1500
  • event_log
  • events
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

It shows on the log that you have provided earlier, the UPS is utilizing the Green Mode feature.  The Green Mode feature gets activated once the unit has detected that you have clean and good input voltage and frequency, thus eliminating the need to use the UPSs other components such as voltage regulation and filtering.  With regards to the other UPS being able to detect power outages, can you check both UPS and see if the Power Quality are set the same i.e. Low, Medium or High.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

APC Smart-UPS SMT1500 1500VA 120V LCD UPS System

Agent: 9.0.1.606

Windows Server 2008 6.0

UPS Model Smart-UPS 1500

Firmware UPS 08.3 / MCU 14.0

these are the logs from the software (the lights in the office all dimmed significantly this morning).

3/12/13 10:33:38 Online (Green Mode) - Entered
3/12/13 09:05:21 Online (Green Mode) - Exited
3/6/13 07:42:08 Online (Green Mode) - Entered
3/6/13 07:42:07 Communication Established


how do i check the event logs on the LCD? (Unfortunately, the unit is in Georgia and

i am in virginia).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:46 PM . Last Modified: ‎2024-03-11 04:31 AM

Sorry, need to add some more information. i bought another unit and it seems to catch

power outages in the event log but does not catch under voltages (unless we are getting

odd problems on internal circuits and not the the feed). So I have two questions and the

first is why would the event log be affected by the sampling interval (problem noticed

on the first unit) and, second, why isn't the second unit catching these voltage fluctuations

(and the first didn't seem to catch them either)?  Sorry if i am making this more complex

than it needs to be but i really didn't like leaving the first UPS on the server when it was

at an out of town location. thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

Can you confirm the model number of your UPS please?  Also, is it the event logs on the LCD or the logs from the software i.e. PowerChute Business or Network Shutdown that you are having problems with?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:47 PM . Last Modified: ‎2024-03-11 04:31 AM

It shows on the log that you have provided earlier, the UPS is utilizing the Green Mode feature.  The Green Mode feature gets activated once the unit has detected that you have clean and good input voltage and frequency, thus eliminating the need to use the UPSs other components such as voltage regulation and filtering.  With regards to the other UPS being able to detect power outages, can you check both UPS and see if the Power Quality are set the same i.e. Low, Medium or High.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore