Hi All
Lightly used (UPS Load is 18.6%) SURTD3000XLI been running for a year, fortnightly self tests OK etc
Today, it went down, (no alert about power loss either) taking the servers with it.
Why would 216 VDC be showing with 74 mins runtime then 216 VDC with 0 mins?
Self Test passed less than 2 weeks ago now cant run for 10 seconds?
Having failed at 0153 it looped around (Battery Disconnected > Sufficient Runtime Available > Battery Reconnected > Insufficient Runtime Available > Battery Disconnected) all day and eventually got to Sufficient Run Time available at 1846 but Self test at 2112 fails?
Seems more than just the battery failing overnight going on???
Any thoughts??
Regards
Rod
Data Logs for the day show:
Battery Voltage at 216 VDC available all day (20 min intervals)
UPS Load at 18-19%
Event Logs as follows (Reverse Order):
11/03/13 21:12:45 Battery Needs Replacing < Device Status is Replace Battery with 0mins at 216.9VDC ??
11/03/13 21:12:45 Self Test Failed
11/03/13 21:12:42 Self Test Initiated < I logged on to check and showed Device Status as Online with 74mins at 216.9VDC
11/03/13 18:46:07 Sufficient Runtime Available
11/03/13 18:46:07 Battery Reconnected
(Like this from 17:38:53 to 18:46:07 )
11/03/13 17:38:53 Insufficient Runtime Available
11/03/13 17:38:53 Battery Disconnected
11/03/13 17:38:53 Communication Established
11/03/13 17:38:53 Monitoring Started < I Turned off power to the UPS and it stopped dead taking servers down again.
11/03/13 16:47:46 Power Restored
11/03/13 16:47:46 Bypass Ended
11/03/13 16:47:28 In User Initiated Bypass < Switched to Bypass via Powerchute
(Like this from 05:58:09 to 16:47:28 )
11/03/13 05:58:09 Battery Disconnected
11/03/13 05:57:30 Sufficient Runtime Available
11/03/13 05:57:30 Battery Reconnected
11/03/13 05:57:09 Insufficient Runtime Available
11/03/13 05:57:09 Battery Disconnected
11/03/13 01:53:17 Communication Established
11/03/13 01:53:17 Monitoring Started
27/02/13 00:11:10 Self Test Passed
27/02/13 00:11:01 Self Test Initiated
22/02/13 20:49:01 Power Restored
22/02/13 20:49:00 Power Failed
17/02/13 15:08:00 Power Restored
17/02/13 14:16:08 Power Failed
13/02/13 00:12:03 Self Test Passed
13/02/13 00:11:54 Self Test Initiated
30/01/13 00:12:56 Self Test Passed
30/01/13 00:12:47 Self Test Initiated
16/01/13 00:13:51 Self Test Passed
16/01/13 00:13:42 Self Test Initiated
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Thanks Liam.
Weird... this week its reporting self tests OK.
Not 100% sure whats going on but APC are sending a new one.
Thanks for the replies.
Regards
Rod
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
If you can get to the UPS serial number via remoting in using PowerChute, you should be able to see the firmware version. if you're using the PCBE console (purple GUI window), make sure that the "show advanced items" or similar is selected on the bottom left hand corner. the UPS firmware version should be listed near the serial number you found. It should be something like 5.1.
Anyway, once we verify that, I can look into it more to see if we think it is a UPS problem or batteries and try to provide an explanation for the behavior you saw.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Hi All
Lightly used (UPS Load is 18.6%) SURTD3000XLI been running for a year, fortnightly self tests OK etc
Today, it went down, (no alert about power loss either) taking the servers with it.
Why would 216 VDC be showing with 74 mins runtime then 216 VDC with 0 mins?
Self Test passed less than 2 weeks ago now cant run for 10 seconds?
Having failed at 0153 it looped around (Battery Disconnected > Sufficient Runtime Available > Battery Reconnected > Insufficient Runtime Available > Battery Disconnected) all day and eventually got to Sufficient Run Time available at 1846 but Self test at 2112 fails?
Seems more than just the battery failing overnight going on???
Any thoughts??
Regards
Rod
Data Logs for the day show:
Battery Voltage at 216 VDC available all day (20 min intervals)
UPS Load at 18-19%
Event Logs as follows (Reverse Order):
11/03/13 21:12:45 Battery Needs Replacing < Device Status is Replace Battery with 0mins at 216.9VDC ??
11/03/13 21:12:45 Self Test Failed
11/03/13 21:12:42 Self Test Initiated < I logged on to check and showed Device Status as Online with 74mins at 216.9VDC
11/03/13 18:46:07 Sufficient Runtime Available
11/03/13 18:46:07 Battery Reconnected
(Like this from 17:38:53 to 18:46:07 )
11/03/13 17:38:53 Insufficient Runtime Available
11/03/13 17:38:53 Battery Disconnected
11/03/13 17:38:53 Communication Established
11/03/13 17:38:53 Monitoring Started < I Turned off power to the UPS and it stopped dead taking servers down again.
11/03/13 16:47:46 Power Restored
11/03/13 16:47:46 Bypass Ended
11/03/13 16:47:28 In User Initiated Bypass < Switched to Bypass via Powerchute
(Like this from 05:58:09 to 16:47:28 )
11/03/13 05:58:09 Battery Disconnected
11/03/13 05:57:30 Sufficient Runtime Available
11/03/13 05:57:30 Battery Reconnected
11/03/13 05:57:09 Insufficient Runtime Available
11/03/13 05:57:09 Battery Disconnected
11/03/13 01:53:17 Communication Established
11/03/13 01:53:17 Monitoring Started
27/02/13 00:11:10 Self Test Passed
27/02/13 00:11:01 Self Test Initiated
22/02/13 20:49:01 Power Restored
22/02/13 20:49:00 Power Failed
17/02/13 15:08:00 Power Restored
17/02/13 14:16:08 Power Failed
13/02/13 00:12:03 Self Test Passed
13/02/13 00:11:54 Self Test Initiated
30/01/13 00:12:56 Self Test Passed
30/01/13 00:12:47 Self Test Initiated
16/01/13 00:13:51 Self Test Passed
16/01/13 00:13:42 Self Test Initiated
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Can you provide the first few digits of the UPS serial number? i.e. IS1012XXXXXX? Also, what is the UPS firmware version?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Also, what is the environment this UPS is installed in? This could be some type of pre-mature battery failure due to a less than ideal environment.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
UPS Model Smart-UPS RT 3000 XL
Firmware Revision 5.1
Manufacture Date 4 December 2010
Serial Number IS1049010478
Battery Replacement Date 12 2010
(The typical expected battery lifetime is three to five years )
The UPS & Servers (2 * HP ML150) live in an open cupboard of a non-airconditioned room.
Data Log Results from last 6 months (our summer)
(Logged at 20minute intervals, 6477 data points)
Input Line Voltage | UPS Output Voltage | Output Frequency | Battery Voltage | UPS Load | Internal UPS Temp | |
(VAC) | (VAC) | (Hz) | (VDC) | (%) | (°C) | |
AVERAGE | 247.2 | 230.1 | 50.0 | 216.3 | 18.6 | 31.1 |
MAX | 256.6 | 230.3 | 50.2 | 235.1 | 20.6 | 37.0 |
MIN | 0.0 | 229.9 | 49.8 | 186.1 | 11.2 | 26.2 |
I'm guessing that an internal temp of 37°C may have been a little excessive? But apparently still within operating temp of 0-40C.
System Status before Self Test (Manual 2 days ago) Current System Status
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Hi Rod,
While the acceptable range for the hardware of the UPS itself is 0°C to 40°C, the batteries should be between 20°C to 25°C to deliver their normal expected service life. The optimum operating temperature for a lead-acid battery is 25 Deg C (77 Deg F). As a guideline, every 8°C (15°F) rise in temperature will cut the battery life in half. A battery which would last for 5 years at 25°C (77°F), will only be good for 2.5 years if operated at 33 °C (95°F). Keep in mind that the battery temperature inside your UPS will always be warmer than the ambient temperature where the UPS is installed.
I have found that in overly warm environments you are more likely to see a sudden failure of the batteries. In your situation it appears that there was a sudden (and total) loss of battery capacity in the time between your biweekly self tests. I would recommend taking your batteries out of production as soon as possible and replacing them with new batteries. Going forward you can either reduce the temperature in the room or plan on proactively replacing batteries on an accelerated schedule.
Hope this helps!
Liam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:30 AM
Thanks Liam.
Weird... this week its reporting self tests OK.
Not 100% sure whats going on but APC are sending a new one.
Thanks for the replies.
Regards
Rod