SmartUPS x 1500 Issues.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS x 1500 Issues.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
115
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:36 AM

0 Likes
6
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:36 AM

SmartUPS x 1500 Issues.

Hey there, 

First time posting, I can't seem to solve this one solo. I'm even having trouble finding the right firmware to update this system. The MODEL is SMX1500RM2UNC and the first 6 of the serial is AS1217. 

 

The system seems to power off at the slightest change in power. I FTP'd in to pull logs and I'm seeing "Failsafe task #50" and "Netsafe Reset" in the debux.txt. 

The following is in the event.txt log :

08/03/2020 09:00:48 UPS: The output power is turned off. 0x0114
08/03/2020 09:00:48 UPS: The output power is now turned on. 0x0113
08/03/2020 09:00:48 UPS: The output power is turned off. 0x0114
08/03/2020 09:00:48 UPS: The output power is now turned on. 0x0113
08/03/2020 09:00:48 UPS: The output power is turned off. 0x0114
08/03/2020 09:00:48 UPS: The power for switched outlet group 3, Outlet Group 3, is off. 0x0186
08/03/2020 09:00:48 UPS: The power for switched outlet group 2, Outlet Group 2, is off. 0x0186
08/03/2020 09:00:48 UPS: The power for switched outlet group 1, Outlet Group 1, is off. 0x0186
08/03/2020 09:00:46 UPS: Restored the local network management interface-to-UPS communication. 0x0101
08/03/2020 09:00:34 System: Network service started. System IP is 192.168.1.92 from manually configured settings. 0x0007
08/03/2020 09:00:29 System: Network Interface coldstarted. 0x0001
08/03/2020 08:54:22 UPS: The output power is turned off. 0x0114

 

This next snippet is from data.txt :

08/03/2020 09:20:30 115.59 116.09 115.68 0.00 0.00 0.00 60.03 100.00 54.18 31.07
08/03/2020 09:10:30 115.50 116.59 115.78 0.00 0.00 0.00 60.01 100.00 54.09 30.90
08/03/2020 08:58:53 114.59 119.00 0.00 0.00 0.00 0.00 0.00 100.00 54.09 30.67
08/03/2020 07:28:19 119.09 119.68 0.00 0.00 0.00 0.00 0.00 100.00 53.87 32.22
08/03/2020 07:18:19 118.68 120.00 0.00 0.00 0.00 0.00 0.00 100.00 54.00 32.29

 

 

For the record after relocating all of the components I had running off of this (0% Load now) the system is staying online.. I'm not sure where to start. I just swapped in fresh batteries just last week and it was working flawlessly.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

Thanks for the insight! I'll see about adding a few things back on to it to see if under a reasonable load it maintains reliability.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

Hi Brandyn,

Can you tell us what you have connected to the UPS?

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

I sure can.

I believe the load was around 60-70%. We have an MD1000 rack mounted storage, and MD3200 rack mounted storage. A Dell r720 server and a Dell r720xd server as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

That load seems very low for that amount of equipment, do all of those units have dual power supplies and if so are all power supplies connected to the UPS or are some of them connected to a mains outlet?

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

I may have misspoken due to having moved all of that equipment off of this APC unit, but those are the main pieces of equipment that are ran on this apc (also a sonicwall and switch/router). The unit running with no load hasn't powered itself down since. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

Hi Brandyn,

It sounds like an overload situation, where the UPS does not have the capacity to run that much equipment it is possible that this can happened even if the UPS does not look overloaded in normal conditions. 

I'll use a really simple example to explain:

1x 1Kva UPS

2x Servers with two power supplies & 600 watt consumption each 

On normal operation each server pulls 300w from the UPS and 300w from the wall, 70% load on the UPS (roughly), now the power goes out and both servers want to pull 600 watts each from the UPS, 140%, the 1Kva UPS can't take this and the load drops.

The same can be true for power variations, the UPS will "clean" the power, the server will detect "clean" and "unclean" power and stop pulling from the wall outlet. 

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:30 AM . Last Modified: ‎2024-03-15 05:35 AM

Thanks for the insight! I'll see about adding a few things back on to it to see if under a reasonable load it maintains reliability.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of