SmartUPS SMT1500i and bad power factor

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS SMT1500i and bad power factor
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
7
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

SmartUPS SMT1500i and bad power factor

Hello,
the SMT1500i has a really low power factor, 1500VA/1kW, around 0.6 power factor.

Am I wrong or this expensive units should be premium one?
Why such a bad power factor?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:24 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:24 AM

On 9/9/2017 9:58 PM, Davide said:

I expect only oremium products and not products with such a bad power factory at such big price.

Nope, I quite like the APC product along side other smaller UPS I have experience with (small being <= 30KVA), I just felt like arguing as it's Saturday night (and according to Elton, Saturday Night's alright for fighting).

I just can't argue with you further as you have zero information to argue against. Expectations don't really count as facts or data I'm afraid.

Have a good weekend though, it sounds like you need a break.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

The answer to your question depends entirely on what and how you are measuring the power factor.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

But the real answer is that with two 12V/18A battery it can do only 980W while other UPS like the Cyberpower Pr1500ELCD with same batteries is capable of 1350W with even a greater runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

On 9/9/2017 6:08 PM, Davide said:

But the real answer is that with two 12V/18A battery it can do only 980W while other UPS like the Cyberpower Pr1500ELCD with same batteries is capable of 1350W with even a greater runtime.

Ahh, I see. You aren't actually measuring anything. You are just complaining about a specification.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

No need to measure anything, APC done it with their bad specs at only 1500/VA 980W and with that runtime

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

On 9/9/2017 6:30 PM, Davide said:

No need to measure anything, APC done it with their bad specs at only 1500/VA 980W and with that runtime

Ahh, ok sorry. I thought you had an actual issue with real hardware, numbers and data rather than having googled a specification sheet and then complained you don't like it. Carry on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:25 AM

Are you some sort of fanboy who defend APC for no real reason apart being a fanboy?

APC is the most expansive brand on the market, I expect only oremium products and not products with such a bad power factory at such big price.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:24 AM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 AM . Last Modified: ‎2024-03-18 01:24 AM

On 9/9/2017 9:58 PM, Davide said:

I expect only oremium products and not products with such a bad power factory at such big price.

Nope, I quite like the APC product along side other smaller UPS I have experience with (small being <= 30KVA), I just felt like arguing as it's Saturday night (and according to Elton, Saturday Night's alright for fighting).

I just can't argue with you further as you have zero information to argue against. Expectations don't really count as facts or data I'm afraid.

Have a good weekend though, it sounds like you need a break.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of