SmartUPS 3000 shuts off or says overload

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 3000 shuts off or says overload
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
2
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

SmartUPS 3000 shuts off or says overload

Hello,

I have a UPS SUA3000R2X180

I have the console cable plugged in and using powerchute to find out what is wrong with this unit. Last December it was functioning correctly, it was unplugged and sat in the bottom of the cabinet untouched for 10 months. We finished our migration and we are now using it to power around 5 servers. When I plugged the unit back in, the unit had a flat line beep and then said overload with no load on it. The overload reset switch does not stick out in the back, and if I unplug the battery and plug it back in, it will work as normal with a battery charge eventually going all the way up. With all of my servers plugged in and powered on the unit only shows about 3 out of 5 lights for the load. Eventually the same with happen, it will say overload and my servers will turn off. Sometimes the unit will display replace battery. As soon as I hold down the test button, it never passes and it will say overload, replace battery or AVR Trim.

I contacted APC support and they had me do a few steps and a brain dead test. The support was quite worthless, at one point the person didnt even read the past history of the ticket. Thier solution is to purchase a new unit.

Nothing has resolved this. I have posted pictures of my powerchute. Maybe someone can help me....





Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

I forgot to get the log. I haven't gone onsite all week since Sat, and tonight I was trying to verify that my backups are executing and forgot to grab the log. I will try to grab tomorrow.


Today, when I tried to do test / power on, all the lights came on. Seemed normal for a few seconds, then shut off. The event log shows nothing other than communication est. disconnected. Battery connected, disconnected. Battery discharged etc...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

Hello,

I have a UPS SUA3000R2X180

I have the console cable plugged in and using powerchute to find out what is wrong with this unit. Last December it was functioning correctly, it was unplugged and sat in the bottom of the cabinet untouched for 10 months. We finished our migration and we are now using it to power around 5 servers. When I plugged the unit back in, the unit had a flat line beep and then said overload with no load on it. The overload reset switch does not stick out in the back, and if I unplug the battery and plug it back in, it will work as normal with a battery charge eventually going all the way up. With all of my servers plugged in and powered on the unit only shows about 3 out of 5 lights for the load. Eventually the same with happen, it will say overload and my servers will turn off. Sometimes the unit will display replace battery. As soon as I hold down the test button, it never passes and it will say overload, replace battery or AVR Trim.

I contacted APC support and they had me do a few steps and a brain dead test. The support was quite worthless, at one point the person didnt even read the past history of the ticket. Thier solution is to purchase a new unit.

Nothing has resolved this. I have posted pictures of my powerchute. Maybe someone can help me....





Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

I forgot to get the log. I haven't gone onsite all week since Sat, and tonight I was trying to verify that my backups are executing and forgot to grab the log. I will try to grab tomorrow.


Today, when I tried to do test / power on, all the lights came on. Seemed normal for a few seconds, then shut off. The event log shows nothing other than communication est. disconnected. Battery connected, disconnected. Battery discharged etc...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore