Multiple Servers Shutdown With Symmetra

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Multiple Servers Shutdown With Symmetra
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
2
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

Multiple Servers Shutdown With Symmetra

Hi Threre,

Our data cetntre is having two identical Symmetra LX UPS(SYAF16KRMI) with
two different mains input sources. All servers connected to the UPS has built-in main/reduntant
power supply units. Main power supply units of all servers are connected to one UPS and the
redundant power supply units of same servers are connected to the other UPS.
Powerchute network shutdwn is used in all servers. As per the current setup servers will start shutdown
even if mains failure is happening in one of the UPS.

We would like to know about a shutdown method wherein servers will shutdown only when both UPS are
on battery or low battery due to mains failure. Is there anyway to achieve this goal?

Awaiting your feedback,

Sajith.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

I'm not a PCNS expert but I don't believe its possible to point a server to two UPS and have it shut down when both UPS batteries are drained. I'll let our PCNS experts give you a positive answer on this. However something to think about:

You have apparently gone some lengths to ensure that your equipment never has an interuption by providing two utility sources and providing 2N backup power to the servers. Typically providing 2 sources of UPS power to a server is for redundancy during an equipment failure and not for prolonged runtime on battery. Saying that I would keep my servers setup to shutdown when the the UPS that powers the Primary power supply reaches its low battery point which you have determined gives your equipment enough time to shutdown.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

upsguy is right. when you install PCNS, you can install it to point to the IP address of each symmetra. the PCNS clients will then only shutdown when both UPSs batteries are drained.

[this article may help as well|http://nam-en.apc.com/app/answers/detail/a_id/3143/]

[these instructions may assist you as well with the install|http://www.apcmedia.com/salestools/PMAR-7X3DAR_R0_EN.zip]

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:28 PM

I'm not a PCNS expert but I don't believe its possible to point a server to two UPS and have it shut down when both UPS batteries are drained. I'll let our PCNS experts give you a positive answer on this. However something to think about:

You have apparently gone some lengths to ensure that your equipment never has an interuption by providing two utility sources and providing 2N backup power to the servers. Typically providing 2 sources of UPS power to a server is for redundancy during an equipment failure and not for prolonged runtime on battery. Saying that I would keep my servers setup to shutdown when the the UPS that powers the Primary power supply reaches its low battery point which you have determined gives your equipment enough time to shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore