SNMP event logged

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMP event logged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
12
2954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

SNMP event logged

I'm in the process of getting all of our UPSs loaded into Zenoss so that I can monitor them via SNMP. I've a few in and I've started receiving warnings on at least one of the UPS which worries me slightly:
"threshold of Bad Battery Packs not met: current value -1.00"

I have had a google around and the closest thing I can find is that the battery constant needs resetting on this UPS, or possibly the battery needs replacing, but it's not reporting it from within the UPS interface nor from the LED display.

Anyone have any knowledge on this?

Cheers

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

hm ok. the 08 in the serial number indicates its from 2008. do you get a lot of battery use/power fluctuations? also, is the rack fairly warm? this could cause the battery to go sooner than it should. i would expect the life of the battery to be 3-5 years but a few factors i mentioned could contribute to earlier failure. lastly, if the battery was stored improperly prior to purchase, either by you or the seller, it could cause an early failure.

since the battery is new, have you ever seen how long the battery lasts when there is a power outage? it could be a cosmetic thing so what you could do is set up a time to do a pull plug test and just let the UPS run on battery to see how long it goes. it is possible the battery may still be good but just require a calibration.

it seems like you have the issue [noted here|http://nam-en.apc.com/app/answers/detail/a_id/1497/].

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

I'll pull it out today and check it. Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

I'm in the process of getting all of our UPSs loaded into Zenoss so that I can monitor them via SNMP. I've a few in and I've started receiving warnings on at least one of the UPS which worries me slightly:
"threshold of Bad Battery Packs not met: current value -1.00"

I have had a google around and the closest thing I can find is that the battery constant needs resetting on this UPS, or possibly the battery needs replacing, but it's not reporting it from within the UPS interface nor from the LED display.

Anyone have any knowledge on this?

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

what did you do when you received this alert? it does not really seem like the constants needs to be reset. it seems like you are trying to change the battery pack count on your UPS to an invalid value - either way, this does not seem like a critical issue.

to investigate further, please provide to me:

β€’ exact model and serial number of the UPS, generally available on the white sticker of the UPS or worst case, from the web interface of the network

β€’ management card (NMC) or SNMP - this will tell me what the valid value should be

β€’ the model of the network management card installed into the UPS that you are reading this value from as well as firmware version

β€’ the OID that you are trying to adjust if you are when this message comes up

β€’ version of the APC MIB you are using

β€’ even.txt and config.ini from the NMC ([instructions here on how to obtain|http://nam-en.apc.com/app/answers/detail/a_id/9321/]

β€’ check in web interface to see what the value is set to under UPS tab->Configuration->General

this should help us get started in the right direction.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

OK, cheers. I'll try and get some new batteries for it and see if that resolves it.

The load power is at 60.3% Watts. Is this what you meant?

FYI, the OIDS that zenoss is using to monitor are:
batteryCapacity 1.3.6.1.4.1.318.1.1.1.2.2.1.0
batteryOutputLoad 1.3.6.1.4.1.318.1.1.1.4.2.3.0
batteryRunTimeRemaining 1.3.6.1.4.1.318.1.1.1.2.2.3.0
iemStatusProbeCurrentTemp 1.3.6.1.4.1.318.1.1.10.2.3.2.1.4.1
upsAdvBatteryNumOfBadBattPacks 1.3.6.1.4.1.318.1.1.1.2.2.6.0
upsAdvBatteryReplaceIndicator 1.3.6.1.4.1.318.1.1.1.2.2.4.0
upsAdvBatteryTemperature 1.3.6.1.4.1.318.1.1.1.2.2.2.0
upsAdvOutputCurrent 1.3.6.1.4.1.318.1.1.1.4.2.4.0
upsBasicBatteryStatus 1.3.6.1.4.1.318.1.1.1.2.1.1.0
upsBasicBatteryTimeOnBattery 1.3.6.1.4.1.318.1.1.1.2.1.2.0
upsBasicConfigNumDevices 1.3.6.1.4.1.318.1.1.1.5.1.1.0
upsBasicOutputStatus 1.3.6.1.4.1.318.1.1.1.4.1.1.0

Message was edited by: The Goatreich

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

yup. sorry, forgot about SNMP.

60% isnt bad, so it is most likely time to get a new battery for this once you verify its age. if its a newer battery from APC, it should have its own serial number on it. the original APC battery will not have one on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:07 AM . Last Modified: β€Ž2024-03-13 11:28 PM

The batteries don't get used very often, literally just in emergency situations, and I can only think of one time in the two years I've worked here where we had a power outage. It is in an air-conditioned room, so the temperature is pretty stable. There have been times where the temperature has risen due to faulty A/C, but not particularly regularly.

I will suggest to my managers about trying the manual runtime calibration as this is holding live servers, which can't be turned of during the day. If that doesn't work then the only option left is a new battery.

Thanks once again for all your help and advice.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

Hi,
sorry I've taken so long to get back about this, and thanks for your reply.

To change the subject very slightly I'd like to shift the attention to another of our UPSs that has a similar problem, but I fear it may be a little more urgent.
Zenoss is our SNMP monitoring tool, and something I'd like to use to receive SNMP traps from our UPS and then send alerts to relevant people in our department if necessary.

At the moment the device has literally just been loaded into the zenoss program, and using the read snmp community.

The error I'm getting through zenoss is:
threshold of Battery Status exceeded: current value 3.00

However I also get e-mail alerts from the same UPS (I intend to phase these out if I can get the snmp tools working). This particular UPS gives the following two errors repeatedly:
Severe - UPS: Batteries discharged.
Informational - UPS: Battery discharge condition cleared.

Model of UPS: SU3000RMINET
Serial Number: YS0415110142
SNMP Card: AP9606
Firmware version of card: v3.0.1
OID: We're not actually trying to adjust this, just use it to monitor. I don't know exactly what OID zenoss is using, but it is part of the Zenpack "APC UPS PowerNet".
MIB: As above
Struggling to get the config.ini, using that link. Presumably because this is an AP9606 not a NMC. I have attached the event.txt. Will look further into this.
Web Interface still looks like the old style on the SNMP cards, underneath the configuration/General section there is only:
UPS Name: UPS_IDEN
Last Battery Replacement: 04/05/04
Audible Alarm: Power Fail
External Batteries: 000


Cheers for your help.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

when was the last time the batteries were changed in your SU3000RMINET? how much runtime is it reporting total? what is your low battery duration set to?

it seems like this is "teetering" between a discharged and charged battery which is most likely the cause of an older, worn out battery, or an improper setting.

the low battery duration setting can be checked under the UPS name, configuration, shutdown parameters, low-battery duration.

the runtime should be under the status section.

and by the way, generally, when a value of -1 is reported via SNMP, it means the OID is not supported.

let me know when you check those settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

I've no idea when the battery was last changed. It's likely to be before my time at the company.
Runtime: 2 minutes
Low battery duration: 2 minutes

Cheers for the info regarding the -1 status. Could prove handy in diagnosing some thing when using zenoss in the future.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

hm ok. makes sense. the serial number indicates the unit is from 2004 so it is possible that the UPS has 6 year old batteries in. how much load percentage is on the UPS?

the low battery duration is the same as the runtime so that is why you are getting these messages. if you have a high load on the UPS or recently added more stuff, this could be a cause and you should low the load (if its like 90-100%).

if it is a low load, its probably time to get a new battery since it has a diminished capacity after 6 years of service (assuming its original) πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

OK, pulled the batteries out. There's a serial number, 3A0839X10272.

I half hoped that just reseating the batteries would resolve the error (we also getting the battery lights flashing in unison on the front panel), but no. I'll still look into replacing them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

0 Likes
0
2952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:08 AM . Last Modified: β€Ž2024-03-13 11:28 PM

hm ok. the 08 in the serial number indicates its from 2008. do you get a lot of battery use/power fluctuations? also, is the rack fairly warm? this could cause the battery to go sooner than it should. i would expect the life of the battery to be 3-5 years but a few factors i mentioned could contribute to earlier failure. lastly, if the battery was stored improperly prior to purchase, either by you or the seller, it could cause an early failure.

since the battery is new, have you ever seen how long the battery lasts when there is a power outage? it could be a cosmetic thing so what you could do is set up a time to do a pull plug test and just let the UPS run on battery to see how long it goes. it is possible the battery may still be good but just require a calibration.

it seems like you have the issue [noted here|http://nam-en.apc.com/app/answers/detail/a_id/1497/].

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore