SmartUPS 3000 repairable?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 3000 repairable?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

0 Likes
9
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

SmartUPS 3000 repairable?

I have a customer with a SmartUPS 3000RM. They got a battery replacement warning but put it off for a couple of weeks, finally replacing the batteries last week. The system has a management card and the management card web interface indicated that the new batteries were installed -- we could see the charge rate going up over time.

They complained about their server restarting and I wondered about the UPS -- management card said everything was OK, but we shut the server down and pulled the utility power from it and off it went.

Batteries were removed, checked for obvious problems (loose terminals, etc) and put back in and the UPS will not turn on at all. Batteries pulled again, checked, swapped position, checked with a voltmeter (showing the right voltage), and still no luck. Utility circuit is good.

My question is -- did I lose something inside? Are these units repairable (logic/control board)? Is there some risk from not replacing batteries when warned? I've had a ton of customers that have put this off (sometimes for months, against my advice, naturally) and never had UPS problems.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • repair
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

I have a customer with a SmartUPS 3000RM. They got a battery replacement warning but put it off for a couple of weeks, finally replacing the batteries last week. The system has a management card and the management card web interface indicated that the new batteries were installed -- we could see the charge rate going up over time.

They complained about their server restarting and I wondered about the UPS -- management card said everything was OK, but we shut the server down and pulled the utility power from it and off it went.

Batteries were removed, checked for obvious problems (loose terminals, etc) and put back in and the UPS will not turn on at all. Batteries pulled again, checked, swapped position, checked with a voltmeter (showing the right voltage), and still no luck. Utility circuit is good.

My question is -- did I lose something inside? Are these units repairable (logic/control board)? Is there some risk from not replacing batteries when warned? I've had a ton of customers that have put this off (sometimes for months, against my advice, naturally) and never had UPS problems.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

Hello,

Please keep this in mind when considering repair of the UPS through Coastal Business Machines (1-888-234-9877). The repair price also factors in a two-year warranty with CBM if anything goes wrong with the UPS. The refurbished unit has only a 90 day warranty. Outside of that, if anything goes wrong, even on the 91st day, you're going to have to replace the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:16 PM . Last Modified: ‎2024-03-15 04:11 AM

That makes very little sense to me. refurbishing an UPS implies that the unit would be just as good as new as worn/old parts have been replaced. And then only give a 90day warranty? Where as, a mere repair of a part would recertify a whole unit with a 2 year warranty?
Besides, as per their website ( http://www.buyupsonline.com/products/smart-ups-3000-rackmount-3u) "Refurbished APC Smart-UPS 3000 Rackmount 3U. Unit is completely reconditioned and will carry a FULL 3 YEAR Bumper-to- Bumper Warranty." It also carries a $549 pricetag. About 50% of the street price of a new APC unit with 2 year warranty.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

And the official answer from APC:
I am sorry to say that, APC do not repair these parts. If you wish you can participate in Trade-UPS program to upgrade your old UPS. In trade Ups you can trade-in your old UPS for a brand new unit and avail the following benefits :
a. Get up to a 35% discount on new APC UPSs.
b. Up to a 35% discount on APC accessories and additional smaller UPSs.
c. Upgrade to two times the VA of your current UPS capacity.
d. Trade in multiple UPSs for larger upgrades.
e. Get up to a 2 year factory warranty on new units.
f. Free removal and/or shipping of existing units.
g. Proper ecological disposal of returned UPSs and batteries for free.


Its amazing that this 'GREEN' ( item g ) effort does not include the repair of the circuit board. It is interesting that the 'GREEN' does result in a refurbish unit. Its not really an ecological green is it.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

Hello,

There is a huge difference in what was being described to you. There have never been repairs on Smart-UPS, as that's what extended warranties are for. The repair cost for the Smart-UPS is actually higher than the price of the refurbished unit, therefore, it's not cost-effective to you. We offer the Trade-UPS program so that you get that unit off of your hands, as well as get the discount off the new UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

it is a big difference. There is no repair price - so how can you compare? And how APC prices them out is what makes it a big difference. Why would you want an extended warranty - apc does not repair them - right ? And the ability to refurbish, but not repair appears to be a bit shady. And the offer to take the unit off your hands could be better served if one were to dispose of unit at local electonic recycling center ( saves gas and all that postage ).

If my UPS broke I want it repaired. I want it repaired for a reasonable cost.

Hence, the topic. AND the reluctant answer: ABSOLUTELY NO!

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

Out of warranty repair on most of our Single-Phase units is around 300-400 dollars. You would want an extended warranty because the unit is replaced Next Business Day. For the Trade-UPS, the unit is sent back to APC, so you receive a new UPS with a new manufacturer's warranty, and WE refurbish it and we pay for the shipping back to us. Maybe there's something I'm missing, but CBM is definitely a better deal on a case-by-case basis, unless of course your UPS is 10 years old.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

are you talking about the Trade UPS program?

if so, [take a look here|http://www.apc.com/recycle/index.cfm]

if not, you can contact coastal business machines if you are looking for repair - www.cbmi.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

I have a Smart Ups 3000 that failed at a remote site (swollen batteries). I replaced sting of batteries with OEM batteries and charged for a day. UPS showed full charge but shuts off when unplugged. UPS fails power up diagnostic most of the time giving audio alarm and battery alarm. After complete visual inspection w/lighted magnifier, I have found R38 & R 43 smoked and cannot distinguish colors or find specs to change. How do I qualify for the exchange program?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

0 Likes
0
3072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:17 PM . Last Modified: ‎2024-03-15 04:10 AM

I have a customer with a SmartUPS 3000RM. They got a battery replacement warning but put it off for a couple of weeks, finally replacing the batteries last week. The system has a management card and the management card web interface indicated that the new batteries were installed -- we could see the charge rate going up over time.

They complained about their server restarting and I wondered about the UPS -- management card said everything was OK, but we shut the server down and pulled the utility power from it and off it went.

Batteries were removed, checked for obvious problems (loose terminals, etc) and put back in and the UPS will not turn on at all. Batteries pulled again, checked, swapped position, checked with a voltmeter (showing the right voltage), and still no luck. Utility circuit is good.

My question is -- did I lose something inside? Are these units repairable (logic/control board)? Is there some risk from not replacing batteries when warned? I've had a ton of customers that have put this off (sometimes for months, against my advice, naturally) and never had UPS problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore