SmartUPS 2200 RM won't turn off loads

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 2200 RM won't turn off loads
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
4
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

SmartUPS 2200 RM won't turn off loads

I have a Smartups 2200 RM, and for years, when I turn off the UPS from the front panel, it shut power off to the loads.

All of the sudden, last night, this changed. Now the loads stay on even after the UPS is off.
How did this change? How can I get change it back?

I run PowerChute Business Edition 7.0.5.
Thanks in advance for any advice.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

I really don't want to spend the money right now. But thanks for the advice.

Is there a procedure to do a "reset to factory defaults" on it? So I can squeek out some more life from it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

A standard smart-ups should certainly power off everything when turned off. Make sure those devices don't have dual power supplies or something drawing from another source. I hate to state the obvious, but is it possible someone moved some power cords? πŸ˜ƒ

There's a model and serial number on the white sticker on the back. Do you mind posting what you have?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

No, there are no dual-power supplies, no changes in the connections. This is in my house and no one has access to it except me.

The unit is a Smart-UPS 2200 RM.
Serial: XS9828003523
Firmware: 82.9.D


I have a recalibration key and I did that procedure last night. The problem remains.

We had a tornado last night. I did my usual power off sequence. All the servers shutdown, then the UPS turned off.
To my amazement, all the routers, switches, monitors, and other stuff were still powered up!

I had to go and pull the plug out of the wall for the UPS to get the loads off.
Its like, after the UPS shutdown, it went to bypass mode. But I don't even know if the 2200 has a bypass mode, nor do I know how to configure it.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

There isn't a bypass mode available for that unit, so there's got to be a problem with it. It's about 10 years old, so it may be time for a new one. Try APC sales support at 800-890-4272, there's a trade-in program you can consider.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:26 AM . Last Modified: β€Ž2024-03-08 02:34 AM

I really don't want to spend the money right now. But thanks for the advice.

Is there a procedure to do a "reset to factory defaults" on it? So I can squeek out some more life from it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore