SmartUPS 1500 Drops Communication (And Restores) at Same Time Nightly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 1500 Drops Communication (And Restores) at Same Time Nightly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:47 AM . Last Modified: β€Ž2024-03-06 02:30 AM

0 Likes
19
4114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:47 AM . Last Modified: β€Ž2024-03-06 02:30 AM

SmartUPS 1500 Drops Communication (And Restores) at Same Time Nightly

I have a SmartUPS 1500 at one of my locations that is managed using the powerchute software from another location. The agent is installed at the location of this smartUPS.

We have a really strange problem, in which the UPS drops communication EVERY evening within a few seconds after 11pm. Of the dozens of these in our enterprise, this is the only one that exhibits this behavior. There are no scheduled tasks on the server, and I have manually set the USB hub to "not power off to conserve energy".

The logs in windows don't seem to provide much assistance either, they say the same thing as the APC log.

Has anyone ever come across this?


9/16/11 00:07:20 Online (Green Mode) - Entered
9/15/11 23:11:29 Communication Established
9/15/11 23:11:23 Communication Lost
9/15/11 23:10:54 Communication Established
9/15/11 23:10:41 Communication Lost
9/15/11 23:10:02 Communication Established
9/15/11 23:09:41 Communication Lost
9/15/11 23:09:06 Communication Established
9/15/11 23:08:53 Communication Lost
9/15/11 23:08:32 Communication Established
9/15/11 23:08:29 Communication Lost
9/15/11 23:08:04 Communication Established
9/15/11 23:07:45 Communication Lost
9/15/11 23:07:29 Communication Established
9/15/11 23:07:13 Communication Lost
9/15/11 23:07:00 Communication Established
9/15/11 23:05:15 Communication Lost
9/15/11 23:04:55 Communication Established
9/15/11 23:04:45 Communication Lost
9/15/11 23:02:14 Communication Established
9/15/11 23:01:25 Communication Lost
9/15/11 23:01:02 Communication Established
9/15/11 23:00:46 Communication Lost

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

USB cables are pretty well shielded and shouldn't require any sort of ferrite bead for interference reduction. The bead (a bit of a misnomer, it's a rectangular box about 1.5" long) shipped with UPS models that used the modular handset cable for communication to external battery packs (I2C bus). It was to keep electrical noise from getting out, not in.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 19
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

I have noticed the same issue on a clients server. They are running Windows Server 2008 R2, UPS is Smart-UPS 1500. They have the same communication lost issue occurring about one or two times a week. It will occur a few seconds after 7:00am or 12:00pm.

I checked all kinds of schedules on the server, and the only thing that corresponded was the Volume Shadow Copy kicking in at those times. You might want to check if that is also happening for you at your 11:00pm time period.

I have not found any solution to the issue or anyway to adjust the sensitivity of the APC/UPS agent losing connectivity. But I am leaning to it being related to the VSC process.

David

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

Ah I understand πŸ™‚

It says Just Smart UPS 1500 in the software, It has configurable outlet groups and also has an LCD screen.

There is not much of anything in the rack, it is located as low as you can go in the rack and the only thing along with it is a single 2u server which is what shows the errors on it at 11pm.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

From the looks of it, it could either be an SMT or SMX unit since these two models are equipped with an LCD.

Like what i_picked_a_winna said, do you have any knowledge if there's any program that might be running around that time that could interfere with the USB communication? How about rebuilding/reinstalling the APC USB device on your device manager?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:30 AM

We've removed and reinstalled the software several times, is there a way I can check the current firmware and if necessary, update it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Since you are using USB, from your device manager it should come up either HID Battery or APC UPS. Which one do you have?

With regards to the firmware, if you are infront of the UPS you can use the LCD display and the buttons to navigate and grab the UPS firmware. It is located under About. The firmware can be updated but you have to call our Technical Support for it requires a special procedure and instructions and should only be done with the rep on the phone.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Anyone got any ideas at all? 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Hi Kruzen,

What method of communication are you using? Is it USB or Serial? From your logs it shows that it happened last September, does it still occur today? Can you also provide the exact model number of the UPS and if it is an SMT/SMX unit can you tell us the firmware that is loaded on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Hey There,

The problem occurs every evening at 11PM on sharp. As mentioned previously, there is no server tasks or scheduled processes also occuring at 11PM. (or just before)

We are using USB, we have the latest version of the powerchute software installed as a server elsewhere in our enterprise and have the agent installed on this server. The two communicate just fine and we manage the UPS through the server software.

9.0.0.613 is the version of the business agent.

The model is a Smart UPS 1500, I'm not sure what more specific I can be abou the model. I also don't know what SMT/SMX means or how to find the firmware model.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

for what JonPro asked for, does it say Smart UPS X 1500 on the unit in the software or just Smart UPS 1500? Do you know if the UPS has an LCD screen or just LEDs? Does it have outlet groups you can configure?

he just wants to know what model UPS it is since we have a few 1500s.

for the overall issue, it does sound like something is always running - what about something that runs around that time thats mounted above or below it in a rack or installed near it that might cause some interference on the USB cable?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

The UPS shows up as APC UPS in device manager.

I've attached a picture to show it's presence in other areas of device manager as well.

Unfortunately this server is about an hour and a half drive away so physical access isn't always easy, doing my best to trouble shoot before heading out there again (we've made several trips to re-connect and check connections trying to diagnose this)

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Hi All, anything else to look at?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

so you were not able to find anything mounted above or below it that runs a task at around that same time? is trying a serial connection to see if it does it to a feasible option?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Correct, there is nothing environmentally/locally located that would effect it at 11pm. I will look into the serial cable. Is there any other ideas I can try while on site?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

well, i have not seen this on this type of UPS with an older firmware or anything. someone asked me about a ferrite bead for something else today randomly and now that is in my mind, i wonder if it would be good to try - if i understand how they work correctly. does the USB cable have one? i havent seen one in a while.

trying a serial cable might be a good option though to rule out the cable and an issue with the USB port on the unit. if you have tried a different USB port, then i am not sure what else to try. i also don't know if its possible to try and move it to a different computer for one night just as a test before we pursue other options like a replacement unit. i know it might be a hassle to do that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

Thanks for all the input..

I'll see if I can put some of the recommendations into practice and get back with more information, you've been super helpful!

Reply

Link copied. Please paste this link to share this article on your social media post.

Unglood_apc
Unglood_apc
Cadet

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:29 AM

I am getting this too.

Every night that the Server Backup runs. At 10:00pm the Backup starts and runs for 5 or 6 hours. Email notifications attached. (How do I stop either the Agent computer or the APC Server notifications. We don't need two).
Strangely enough there are also email notifications at 6:15am when Backup is not happening.

It's an SMT1500RM2U
It's on a Dell PowerEdge 2850 (W2K3) - you know Dell's always solid with their USB ports!!
I suspect moving the USB drive to a W2K8 Server is the quickest way to go on this.
There is also an SMT1500RM2U on a W2K8 member server. Never a glitch!

So, Why the APC comms lost over USB and How to stop dupl;icate emails?

Thanks.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:25 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:48 AM . Last Modified: β€Ž2024-03-06 02:25 AM

if you go into the email configuration for powerchute business edition, it should allow you to edit your email notifications and disable/enable which ones you want. i think what your issue is that you have email configured using the powerchute business edition Agent web interface and then you also are using the powerchute business edition console GUI. only one or the other should be used to manage the UPS so you just need to disable one of these email alerts. are you familiar with accessing the web agent via https://:6547? the console is probably a program located in your start menu and opens in a purplish GUI versus the web browser.

Reply

Link copied. Please paste this link to share this article on your social media post.

Unglood_apc
Unglood_apc
Cadet

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

Thanks for the tip on disabling the alerts. I disabled on the Web interface of the directly connected USB server. Now I only get 3 "Communication Lost" emails a night (10:30pm, 2:15am and 6:30am) instead of 6. Progress indeed!

In response to David's post above, "I have not found any solution to the issue or anyway to adjust the sensitivity of the APC/UPS agent losing connectivity. But I am leaning to it being related to the VSC process." There is no VSC process happening on the Server here in question. It is a (Dell) W2K3 DC, file server and Backup to USB server.

I think it must be related to the Backup in as much as this doesn't happen on the weekend! The Backup is just a simple xcopy batch file/script.

This communication does not occur on a (Dell) W2K8 Server with no backup occurring.

Does anyone have any solution to this irritating APC UPS agent losing USB connectivity to it's host? (Disabling the email alert is not a solution but, a workaround)

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

0 Likes
0
4116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:49 AM . Last Modified: β€Ž2024-03-06 02:25 AM

USB cables are pretty well shielded and shouldn't require any sort of ferrite bead for interference reduction. The bead (a bit of a misnomer, it's a rectangular box about 1.5" long) shipped with UPS models that used the modular handset cable for communication to external battery packs (I2C bus). It was to keep electrical noise from getting out, not in.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore