APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:48 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:48 AM
My SmartUPS 1250 has developed a problem. When turning it on, it passes the self test. Batteries are charged to 100%. After a few minutes it starts cycling to battery power for about a second, beeping twice, then goes back to line. In about 2 more seconds, the cycle repeats again. It continues cycling between AC and battery power indefinitely. After a while, the time on AC is just a fraction of a second. It spends a few seconds on battery, switches to AC for just a moment, then back to battery. The AC power is perfectly fine - exactly 120 volts, no glitches. (Other UPS's on the same circuit are not having any problems)
Has anyone heard of this problem? Is there any fix?
Is there any service information or diagnostic procedures available for this model? It has been very reliable, and the batteries are relatively new, so I hate to throw it into the dumpster.
Message was edited by: timg11
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:59 AM . Last Modified: 2024-03-08 03:47 AM
Anytime! I appreciate you giving us updates on the situation; the information is helpful.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:47 AM
Hello:
This does sound strange indeed. Just a few questions, though. Firstly, do you have any type of serial cable attached to this? A dangling cable can often send erroneous signals to the UPS. If not, have you tested the UPS by itself with no load attached, to see if it shows the same symptoms? Have you tried a different outlet on this circuit?
Lastly, there is a "sensitivity" option on this UPS (as well as most APC UPS's) which is worth taking a look at. To lower the sensitivity on this particular unit, you can use the dip switch (Option 1 dip switch...far right) on the back. Setting this switch to the "On" (up) position will lower the sensitivity of the UPS, making it less picky to input line distortion/harmonics. Considering that you have explained that other UPS's on the same circuits are working fine and your input appears clean, this does not appear to be the issue in this case. However, it is always worth a shot for the sake of troubleshooting.
Let us know how it all works out!
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:47 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:47 AM
Thanks for the reply. No there was no serial cable attached. I did connect a serial cable to a terminal program to see if there was any clues. When it goes into the cycling mode, I see a series of !$!$ characters being sent by the UPS.
I am testing it with no load. It has the same behavior.
Very clever idea about the DIP switch. I set switch 1 to On, and so far (within 10 minutes) the UPS has not started cycling. Previously, it started cycling within 2 minutes.
Maybe the internal comparator components have drifted in value enough to make it think good power is bad, but the components in the less sensitive setting have not drifted as far off?
I'll let it go for a day or so and see if it stays up.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:59 AM . Last Modified: 2024-03-08 03:47 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:59 AM . Last Modified: 2024-03-08 03:47 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:59 AM . Last Modified: 2024-03-08 03:47 AM
It's been working OK for a day now with no load, so I think it is a good solution for this problem.
I'll hook the loads up to it again later when I can shut everything down to do the transfer and let you know if that causes any problems.
Thanks for the suggestion!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:59 AM . Last Modified: 2024-03-08 03:47 AM
Anytime! I appreciate you giving us updates on the situation; the information is helpful.