SmartUPS 1250 cycles on/off line when AC power is present.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 1250 cycles on/off line when AC power is present.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:48 AM

0 Likes
5
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:48 AM

SmartUPS 1250 cycles on/off line when AC power is present.

My SmartUPS 1250 has developed a problem. When turning it on, it passes the self test. Batteries are charged to 100%. After a few minutes it starts cycling to battery power for about a second, beeping twice, then goes back to line. In about 2 more seconds, the cycle repeats again. It continues cycling between AC and battery power indefinitely. After a while, the time on AC is just a fraction of a second. It spends a few seconds on battery, switches to AC for just a moment, then back to battery. The AC power is perfectly fine - exactly 120 volts, no glitches. (Other UPS's on the same circuit are not having any problems)

Has anyone heard of this problem? Is there any fix?

Is there any service information or diagnostic procedures available for this model? It has been very reliable, and the batteries are relatively new, so I hate to throw it into the dumpster.

Message was edited by: timg11

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

Anytime! I appreciate you giving us updates on the situation; the information is helpful.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:47 AM

Hello:

This does sound strange indeed. Just a few questions, though. Firstly, do you have any type of serial cable attached to this? A dangling cable can often send erroneous signals to the UPS. If not, have you tested the UPS by itself with no load attached, to see if it shows the same symptoms? Have you tried a different outlet on this circuit?

Lastly, there is a "sensitivity" option on this UPS (as well as most APC UPS's) which is worth taking a look at. To lower the sensitivity on this particular unit, you can use the dip switch (Option 1 dip switch...far right) on the back. Setting this switch to the "On" (up) position will lower the sensitivity of the UPS, making it less picky to input line distortion/harmonics. Considering that you have explained that other UPS's on the same circuits are working fine and your input appears clean, this does not appear to be the issue in this case. However, it is always worth a shot for the sake of troubleshooting.

Let us know how it all works out!


Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:58 AM . Last Modified: β€Ž2024-03-08 03:47 AM

Thanks for the reply. No there was no serial cable attached. I did connect a serial cable to a terminal program to see if there was any clues. When it goes into the cycling mode, I see a series of !$!$ characters being sent by the UPS.

I am testing it with no load. It has the same behavior.

Very clever idea about the DIP switch. I set switch 1 to On, and so far (within 10 minutes) the UPS has not started cycling. Previously, it started cycling within 2 minutes.
Maybe the internal comparator components have drifted in value enough to make it think good power is bad, but the components in the less sensitive setting have not drifted as far off?

I'll let it go for a day or so and see if it stays up.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

timg11 wrote:
Very clever idea about the DIP switch. I set switch 1 to On, and so far (within 10 minutes) the UPS has not started cycling. Previously, it started cycling within 2 minutes.
Maybe the internal comparator components have drifted in value enough to make it think good power is bad, but the components in the less sensitive setting have not drifted as far off?
These were my thoughts exactly. In your situation, obviously your power has not changed any and your other units are operating fine. Considering the age of the unit (we haven't made the 1250's in quite some time, so I'm assuming your's is 10-15 years old) I'm thinking that perhaps the values have caused that to be a bit too picky, thinking power is bad when in fact it is not.

I hope this helps, and I hope your unit continues to work with this setting! I'm sure you've become quite attached to that if you've owned it since it was new. πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

It's been working OK for a day now with no load, so I think it is a good solution for this problem.
I'll hook the loads up to it again later when I can shut everything down to do the transfer and let you know if that causes any problems.
Thanks for the suggestion!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 04:59 AM . Last Modified: β€Ž2024-03-08 03:47 AM

Anytime! I appreciate you giving us updates on the situation; the information is helpful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.