General PowerChute Business, PowerChute Network Shutdown and NMC2 Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • General PowerChute Business, PowerChute Network Shutdown and NMC2 Card
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

0 Likes
5
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

General PowerChute Business, PowerChute Network Shutdown and NMC2 Card

Hello everyone,

We have been using the a few unit SMT1500 for the past 3 years and we are happy with the product.

We recently upgraded our little server and decided to go for the rack-mount SMX1500 which has the network management card 2 to communicate with the server.

This is the first time we installed the Network Shutdown but unsure if we do understand it correctly. So when the power is down, and our server runs from the battery, after the "X" amount of minute, the PowerChute Network shutdown will actually "shutdown" our Windows 2019 server? How does it do that? Or, we must write a shutdown-script and setup the software to run the script?

And how about the PowerChute Business edition? Is it similar to the Network shutdown or something else? What is it for?

We are a little confused so everyone could give us some hint, we would be appraised.

Thank you for our newbie questions, and we appreciated your patience.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

Hi,

You can add up to 5 SMX48RMBP2U 

https://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SMX1500RM2U&family_id=165

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

Hi,

On 4/27/2020 11:27 PM, James said:

This is the first time we installed the Network Shutdown but unsure if we do understand it correctly. So when the power is down, and our server runs from the battery, after the "X" amount of minute, the PowerChute Network shutdown will actually "shutdown" our Windows 2019 server? How does it do that?

PowerChute Network Shutdown works in conjunction with the Network Card. You can configure events within PowerChute to start OS shutdown after the UPS has run on battery for x minutes or when the battery has x amount of runtime remaining. Open the PowerChute web interface and go to Configure Events. There you will see UPS on Battery and Runtime remaining below threshold. If you click on the ? the help file will launch and you will see a description of each event. Also, see Schneider Electric FAQ FA326148 

h1nNQQ%2B33ErsO3IHom0wSA%3D%3D.pngh1nNQQ%2B33ErsO3IHom0wSA%3D%3D.png

If you do not configure an event within PowerChute the OS will be powered down when the UPS reaches the low battery threshold. The network card will report the UPS has reached low battery and the PowerChute client will command the OS down. See Schneider Electric FAQ FA405707 for an explanation of the low battery setting.

On 4/27/2020 11:27 PM, James said:

And how about the PowerChute Business edition? Is it similar to the Network shutdown or something else? What is it for?

You would not install PowerChute Business Edition on an OS that is running PowerChute Network Shutdown. If you have installed PowerChute Network Shutdown on an OS and attempt to install PowerChute Business Edition the installer warns you that Network Shutdown is installed the installation will fail. The same will happen if they have installed Business Edition on an OS and attempt to install Network Shutdown. 

PowerChute Network Shutdown communicates with the UPS through the Network card via the LAN. PowerChute Business Edition communicates with the UPS via USB or Serial cable. When running Networm Shutdown management of the UPS is done via the Network card. When running Business Edition management of the UPS is done via PowerChute since there is no direct connection to the UPS.

When utilizing Business Edition, you are limited to the number of servers that can be powered down. Usually 3 unless a command file has been deployed. When utilizing Network Shutdown if pushed to the extreme you can power down 12700 servers. I don't recommend configuring 12700 servers with a single UPS, but it can be done. See Schneider Electric FAQ FA159540 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

Hey Bill,

Thank you very much for your 101 into the APC world.

So if we setup correctly, the Network Shutdown will issue "shutdown" command to the Windows Server 2019, and the server would be shutdown properly as if we did it ourselves, is that correct?

And one more thing that I realize from your screen shot: Our Network shutdown > Configure Events does not have the column called "Notification" (I attached ours one here for your reference). We installed the latest version of the Network shutdown already.

How do I enable this column Notification then?

Thank you very much for your patience

Regards

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:48 AM

Hi,

On 4/28/2020 11:31 AM, James said:

So if we setup correctly, the Network Shutdown will issue "shutdown" command to the Windows Server 2019, and the server would be shutdown properly as if we did it ourselves, is that correct?

Yes. That is correct.

On 4/28/2020 11:31 AM, James said:

How do I enable this column Notification then?

The screenshot I provided was of PowerChute running on a Linux OS. Notification is not available in PowerChute on Windows. We do have FAQ FA239561. You can use the command file attached to the FAQ to enable messaging for Windows OS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

Thank you very much for your help Bill.

I have just one more question, regarding to the extra batter. According to the user manual, I see that we can only (or the manual only mention) add 1 extended battery to prolong the run time. Could we add 2 extended batteries to the SMX system?

Thank you again, for your helps

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:58 AM . Last Modified: ‎2024-03-08 03:47 AM

Hi,

You can add up to 5 SMX48RMBP2U 

https://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SMX1500RM2U&family_id=165

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of