Hi,
I have a problem with a Smart VT 20kVA
The UPS functions without problem on utility service, but when switching to genset it displays a "Site Wiring Fault" problem and goes in battery mode.
The UPS User Manual says that this is a: "Wrong phase rotation on the input side. The UPS will continue to supply conditioned power from batt." I measured phase rotation with a Fluke 9062 Motor and Phase Rotation Indicator and determined that phase rotation was proper.
Can it be another possible reason for this to happen? I read from other posts that Symmetra LX also displays this fault when neutral cable isn't detected or when there is a difference in voltage more than 10% between phases, is this the same case?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:03 AM . Last Modified: 2024-03-19 01:12 AM
It is clockwise.
Ph-Ph ~380V
Ph-N ~220V
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:03 AM . Last Modified: 2024-03-19 01:12 AM
You said the rotation is correct. Is it clockwise or counter clockwise? What is the voltage of Ph - Ph and Ph - N.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:03 AM . Last Modified: 2024-03-19 01:12 AM
It is clockwise.
Ph-Ph ~380V
Ph-N ~220V
Link copied. Please paste this link to share this article on your social media post.