Smart-UPS serial communication

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS serial communication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
9
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Smart-UPS serial communication

Hi,

I have a Smart-UPS 3000LCDRM2U installed and try to setup the serial connection to an old Solaris 9 system.

Same machine worked with an old Smart-UPS 3000 (without LCD) and the old PowerChute Plus software without problems until the UPS died.

The new UPS will not communicate with PowerChute Plus or PowerChute Business Edition 8-9.0.1.

I already tried baud rates 2400, 9600, 19200, but no communication established.

Do I need to enable the serial port at the UPS first?

And if, how?

I dont have direct access to the UPS, only remote access to the server, and I am not familiar with the setup at the UPS front panel!

Thanks for help

Guenter

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • communication
  • serial
  • smart-ups
  • solaris
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Thanks for sharing what did work for you. That is strange since that UPS communicates at 9600..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Can you confirm what serial cable part number you have in use? Can you also confirm the exact model of the UPS? I am thinking it starts with SMT or SMX which definitely requires PowerChute Business Edition v8.5.1 or higher to support communications with SMT or SMX model UPSs.

I am not sure about other specifics on Solaris. Bill P. - anything else you could add?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

The UPS model is: SMT3000RMI2U

The serial cable part number is: 940-0625A

I have restartet the UPS and the server, the server serial device is ttyb which is configured in the software.

Also I tried several different settings on the serial interface on the server.

So far I know is the serial setting of the UPS 9600-8N1.

At the moment I am trying PCBE 9.0.1 (the last one for Solaris?), I can switch back to 8.5.1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

The test with PCBE 8.5.1 has the same result: no communication.

I also tested the PCBE settings for SMT,SMX and also for Smart-UPS, which one is the correct one for this UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Hi,

The last version on PCBE to support Solaris 9 is version 8.0.1. Unfortunately your Smart-UPS is not compatible with version 8.0.1. Your option is to purchase our legacy communication card and then you can continue to run PowerChute Plus or install PCBE 8.0.1. I would recommend using PC+ since that is what you are familiar with. Here is a link to the cards web page Buy Legacy Communications SmartSlot Card - Technical Specifications and Information | APC

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

The readme.txt of the PCBE 8.5.1 stated this:

     The PowerChute Business Edition Agent is compatible with Solaris 9 and Solaris 10

Now you say the last version for Solaris 9 is PCBE 8.0.1.

What is correct now?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Another question:

the firmware level of the new UPS is 8.3.

Is this ok for the legacy communications card?

Or is a firmware upgrade needed? I could'nt find anything about this.

I ask, because the customer is able to install the card and the cables, but not the firmware.

For this I have to drive some hundred kilometers.

Edit: firmware version

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Yes, the firmware will be fine. Here is the LCC compatibility chart -> AP9620 Legacy Communications Card (LCC) Compatibility | FAQs | Schneider Electric US

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Now I got it up and running! laughing

It is still Solaris 9 and it is running with PCBE 9.0.1!!!

For any future records: What it needs for correct setup was:

1. Setup the eeprom for ttyb

# eeprom | grep ttyb

ttyb-rts-dtr-off=true

ttyb-ignore-cd=false

ttyb-mode=2400,8,n,1,-

!! reboot !!

2. Setup ttyb in SMC (Solaris Management Console)

Baud rate: 2400, software handshake, Initialize only

Thanks for your help and have a nice weekend!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:21 AM . Last Modified: ‎2024-03-05 02:22 AM

Thanks for sharing what did work for you. That is strange since that UPS communicates at 9600..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore