Smart-UPS X 3000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
RafalS1
Crewman RafalS1
Crewman

Posted: ‎2024-10-15 01:01 AM

0 Likes
7
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 01:01 AM

Smart-UPS X 3000

Hello, we have Smart-UPS X 3000 with 3 batteries, recently it has been switching to battery quite often for few seconds due to distorted input. 

RafalS1_0-1728978916257.png

We had an electrician come over and test all the cables, we use commando sockets to power the UPS. He did not find any issues in cables, he switched the UPS to a different socket, no change, he also checked the mains to the building. No issues. Users also did not report any power loss in the building. 

Here is the status:

RafalS1_1-1728978994324.png

When done a self test, it passes.

Is there anything else we could try?

I've attached the data log. 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-15 04:31 AM

0 Likes
0
1154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 04:31 AM

Based on the information you provided in the data logs this site is experiencing (Dirty Power) as defined by your user settings.

 

The site is seeing out of band voltage & frequency and possible THD. As such is going into battery only mode as designed and defined by you / user / default settings.

 

You may consider adjusting the Power Quality (Sensitivity) which impacts when the system will go into battery only mode.

 

Doing so will provide the cleanest power to the attached devices but will sacrifice battery service life.

 

You may consider adjusting the upper and lower input voltage transfer levels. Doing so will cause the system to enter into AVR mode.

 

Meaning the system will Trim / Boost the incoming voltage input and inverse the same on the output to a defined level.

 

The AVR mode is the best balance of power quality output while preserving battery service life.

 

Make the changes as outlined above and monitor the site for behaviour.

 

Keeping in mind you need to validate the attached equipment can tolerate the dirty power without locking up and expect an increase in power consumption.

 

If you have more questions please do ask. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

RafalS1
Crewman RafalS1
Crewman

Posted: ‎2024-10-15 06:52 AM

0 Likes
1
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 06:52 AM

Hi Teken,

 

Thank you for reply and help with another case. Im not an electrician so I'm not sure what should be the values, please see below current values, could you advise please how to adjust it as you advised?

 

RafalS1_0-1729000082378.png

Cant see anywhere where to enable AVR mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-16 02:15 AM . Last Modified: ‎2024-10-16 02:48 PM

In response to RafalS1
0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-16 02:15 AM . Last Modified: ‎2024-10-16 02:48 PM

Hi,

 

Please confirm what the input line voltage is for your region?!? Is it 230 as seen in the screen capture or 220/240 VAC?

 

AVR: The AVR circuit is managed by the two boxes labeled output. We can make some changes once you confirm the input voltage for your specific region.

 

Please keep in mind (IF) the input voltage needs to be changed. The UPS may have to be rebooted and will disconnect all connected loads.

 

So please ensure those devices are powered down if you need to make that change. 

Reply

Link copied. Please paste this link to share this article on your social media post.

RafalS1
Crewman RafalS1
Crewman

Posted: ‎2024-10-16 06:11 AM

0 Likes
1
1079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-16 06:11 AM

The standard voltage in the region is 230V, Although you are right looking at the log it has been jumping up and down. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-17 04:38 AM . Last Modified: ‎2024-10-17 04:39 AM

In response to RafalS1
0 Likes
0
1074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 04:38 AM . Last Modified: ‎2024-10-17 04:39 AM

Please review the user manual on page 13-14. There are three possible options to select and change to reflect your input power environment.

 

https://download.schneider-electric.com/doc/SPD_EALN-7T5L2F_EN/SU%20UM%20990-3651H%20MN01%20EN.pdf

 

Local Power Quality, Sensitivity, Upper / Lower Input transfer voltage.

 

You may try to adjust the local power quality first to FAIR vs Good. You may Also adjust the sensitivity from NORMAL vs REDUCED.

 

I would only adjust the power quality as a first step and monitor. As noted insure the attached equipment is designed to accept the wider input (dirty power).

 

Let me know how it all turns out. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

RafalS1
Crewman RafalS1
Crewman

Posted: ‎2024-10-23 08:35 AM

0 Likes
1
964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 08:35 AM

Hi Teken,

 

I believe local power quality settings are only available during the initial setup?

 

I've however changed the sensitivity from normal to reduced that greatly reduced the number of battery switch, since Thursday we had only 1 switch. Just wonder how that will affect the batteries, we have 3 in total connected to that UPS. We plan to replace that UPS next year. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-24 08:06 AM

In response to RafalS1
0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 08:06 AM

Generally speaking the long term service life will be reduced. The average service life is 2-5 years based on usage, temperature, and environmental conditions.

 

As noted you may also adjust the upper & lower transfer voltage. Doing so will cause the system to use the AVR circuit to trim / boost the output if and when the input voltage is out of band.

 

Doing so will extend the battery service life because the system will only go into battery only mode if there is a grid down event / lights out.

 

Or if the threshold has been met by your user defined settings. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore