APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
I have recently installed this unit and I am getting these emails quite often now, often in very quick succession, with a 1 second or less gap.
Logs below from one of many instances this happens:
22/11/15 | 23:47:26 | 241.7 | 241.7 | 135.7 | 100 | 50.0 | 50.0 | 13.5 | 28.3 |
22/11/15 | 23:27:26 | 240.8 | 240.8 | 135.7 | 100 | 50.08 | 50.08 | 13.5 | 28.4 |
22/11/15 | 23:07:26 | 240.1 | 240.1 | 135.8 | 100 | 50.0 | 50.0 | 13.6 | 28.1 |
22/11/15 | 22:47:26 | 239.1 | 239.1 | 135.7 | 100 | 50.0 | 50.0 | 13.4 | 28.5 |
22/11/15 | 22:27:26 | 240.3 | 240.3 | 135.7 | 100 | 50.0 | 50.0 | 13.5 | 28.5 |
22/11/15 | 22:07:26 | 238.9 | 238.9 | 135.7 | 100 | 50.0 | 50.0 | 13.5 | 28.5 |
22/11/15 | 21:47:26 | 238.2 | 238.2 | 135.6 | 100 | 50.08 | 50.08 | 13.4 | 28.7 |
22/11/15 | 21:27:26 | 237.4 | 237.4 | 135.6 | 100 | 50.0 | 50.0 | 13.5 | 28.6 |
22/11/15 | 21:07:26 | 237.2 | 237.2 | 135.6 | 100 | 50.0 | 50.0 | 13.4 | 28.8 |
22/11/15 | 20:47:26 | 235.9 | 235.9 | 135.6 | 100 | 49.98 | 49.98 | 12.7 | 28.7 |
22/11/15 | 20:27:26 | 236.9 | 236.9 | 135.6 | 100 | 49.98 | 49.98 | 12.6 | 28.9 |
22/11/15 | 20:07:26 | 237.4 | 237.4 | 135.6 | 100 | 49.98 | 49.98 | 12.6 | 28.8 |
22/11/15 | 19:47:25 | 237.9 | 237.9 | 135.6 | 100 | 49.98 | 49.98 | 12.7 |
29.0 |
Windows logs:
- | System |
|
|
|
|
|
|
|
|
|
|
- | EventData |
"UPS On Battery" |
- | System |
|
|
|
|
|
|
|
|
|
|
- | EventData |
"Utility Power Restored" |
The outage shown in the windows logs is at 9:00:45 PM (time is adjusted for Daylight savings) and the UPS logs are for the same time period.
I am using USB to connect.
Any trouble shooting tips?
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Thanks, I have changed that now and will report back in 24hrs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Hi Alex,
The UPS is likely seeing some brief dirty power and transfers onto battery during this time. To limit the amount of times this happens you can change the sensitivity setting on the unit to low. This will allow a wider range of input voltage to pass to your equipment before transferring onto battery.
-Mike
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-30 11:06 PM . Last Modified: ‎2024-03-06 03:24 AM
Thanks, I have changed that now and will report back in 24hrs.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.