APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:12 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:12 PM
I have a new Smart-UPS X 3000. Are the network management cards hot swappable?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:11 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:11 PM
Thank you very much for the quick reply Angela.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:12 PM
Hello,
Yes, they are. See this knowledge base article for additional detail -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156132
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:11 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:33 AM . Last Modified: 2024-02-29 11:11 PM
Thank you very much for the quick reply Angela.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.