"UPS: RFC1628 MIB UPS is on battery" message every 2 minutes

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "UPS: RFC1628 MIB UPS is on battery" message every 2 minutes
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

0 Likes
3
5293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

"UPS: RFC1628 MIB UPS is on battery" message every 2 minutes

Hello,

starting yesterday my UPS APC 3000VA is sending me this message every 2 minutes:

"Code : 0x3601

Informational - UPS: RFC1628 MIB UPS is on battery."

I have logged into the web interface and could not find any problems there; no error or alarms in UPS status or logs.

Also, I have physically checked the UPS and it works well, providing power and passing the self test, all LEDS green.

I have tried rebooting it, turning it on and off, runnning self tests, clearing the logs, but with no result.

I keep getting that e-mail message every 2 minutes.

Any suggestions?

Thank you,

Mihail 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • battery
  • is
  • mib
  • on
  • rfc1628
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

0 Likes
0
5290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

Hi Mihail,

Yes, I am just suggesting you disable the "RFC1628 MIB" alarm group/category messages specifically. All other messages would still come through and shouldn't be modified and will cover what you're looking for as far as UPS status, alarms, etc.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

0 Likes
0
5290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

You'll probably want to disable this event from being emailed/logged if you aren't using SNMP and don't have any idea what the UPS RFC1628 Generic SNMP MIB is.

Here is some information on it -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156148 

This is just getting sent to you when your UPS goes on battery in addition to the normal "on battery" notification. You can disable this alarm under the Configuration -> Notification ->Email->Event actions/by group menu in v6.X.X firmware or under Administration->Notification sub tab->Event Actions by group and disable the RFC1628 events for email (and event log if you want).

Hope that helps. This is just more of a nuisance alarm for you so you don't have to worry that your UPS has a problem. Just need to disable it and stop the nuisance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

0 Likes
0
5290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

Thank you for answering !

If I follow your suggestion, will I still receive by e-mail a notification when the UPS really works on battery (in the event of a power failure)?

I need these types on notifications so I can track how often power failures occur and how soon the diesel generator kick in.

Thank you!

Mihail

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

0 Likes
0
5291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:33 AM . Last Modified: ‎2024-02-29 11:12 PM

Hi Mihail,

Yes, I am just suggesting you disable the "RFC1628 MIB" alarm group/category messages specifically. All other messages would still come through and shouldn't be modified and will cover what you're looking for as far as UPS status, alarms, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore