Smart-UPS X 3000: Power Factor Correction Fault after losing input power
  • Smart-UPS X 3000: Power Factor Correction Fault after losing input power
Posted: ‎2021-06-29 08:49 AM . Last Modified: ‎2024-03-12 02:45 AM
3460
After losing input power to this UPS, it now won't power on correctly again. The warning led becomes red, all others are off.
We have a management card attached and can access it. We see the warning message A power factor correction fault exists.
This prevents me from turning output power on or running a self test.
When I try to turn the UPS off and on again, it comes back to the same state, and the logs say:
21.10.201410:28:22UPS: A power factor correction fault exists.
21.10.201410:27:52UPS: A power factor correction fault no longer exists.
21.10.201410:27:29UPS: A power factor correction fault exists.
Current input voltage seems to be normal: Input Voltage: 230.7 VAC
Status from CLI:
apc>ups -st
E000: Success
State: Off, PFC Fault
apc>detstatus -all
E000: Success
Status of UPS: Off, PFC Fault
Last Transfer: None
Input Status: Voltage too low
Runtime Remaining: 18 hr 12 min 15 sec
Battery State Of Charge: 99.9 %
Output Voltage: 0.0 VAC
Output Frequency: 0.0 Hz
Output Watts Percent: 0.0 %
Output VA Percent: 0.0 %
Output Current: 0.00 A
Output Efficiency: -- %
Output Energy: 1179.909 kWh
Input Voltage: 231.4 VAC
Input Frequency: 50.1 Hz
Battery Voltage: 124.8 VDC
Battery Temperature: 27.4 C, 81.3 F
Self-Test Result: Refused via management device due to invalid state
Self-Test Date: 10/20/2014
Calibration Result: Unknown
Calibration Date: 02/06/2014
Any idea, can we fix this quickly?
  • fault
  • pfc
  • problem
Thanks for the update. Yes, this type of fault requires a replacement typically.
Update: I got hold of APC support, and they will send a replacement unit.