Hey guys
So I got the following message in the "Recent Device Events":
06/18/2019 19:26:29 UPS: The output power is turned off.
06/18/2019 19:26:29 UPS: The graceful shutdown period has ended.
06/18/2019 19:26:29 UPS: No longer on battery power.
06/18/2019 19:26:29 UPS: A backfeed relay fault exists.
06/18/2019 19:26:28 UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
(The date is misconfigured at the APC, the log is from yesterday evening).
The client told me that the APC is beeping and the servers attached to it got a orange blinking powersupply. What's also a bit weird is that under "Outlet Group Control" are outlets are in a "Off"-State, I didn't configure the APC so I don't know about the setup, but is that normal?
As I don't got that much experience with APC's so can anyone of you tell me what might cause the error?
Recent activities in the data log show the following:
Date Time Vmin Vmax Vout Iout %Wout %out FrqOut %Cap Vbat Tups T1ambC %Hum1 T2ambC %Hum2
06/18/2019 21:48:06 237.94 239.70 0.00 0.00 0.00 0.00 0.00 100.00 131.81 +24.99 21.0
06/18/2019 21:38:06 237.16 239.20 0.00 0.00 0.00 0.00 0.00 100.00 132.00 +25.03 21.0
06/18/2019 21:28:06 232.23 238.00 0.00 0.00 0.00 0.00 0.00 100.00 132.19 +25.11 20.0
06/18/2019 21:18:06 235.50 238.09 0.00 0.00 0.00 0.00 0.00 100.00 132.38 +25.21 21.0
06/18/2019 21:08:06 234.64 241.47 0.00 0.00 0.00 0.00 0.00 100.00 132.59 +25.27 21.0
06/18/2019 20:58:06 236.13 241.31 0.00 0.00 0.00 0.00 0.00 100.00 132.78 +25.37 20.0
06/18/2019 20:48:06 235.81 238.13 0.00 0.00 0.00 0.00 0.00 100.00 133.00 +25.52 21.0
06/18/2019 20:38:06 236.19 237.77 0.00 0.00 0.00 0.00 0.00 100.00 133.25 +25.63 21.0
06/18/2019 20:28:06 235.28 238.50 0.00 0.00 0.00 0.00 0.00 100.00 133.47 +25.77 20.0
06/18/2019 20:18:06 236.58 238.78 0.00 0.00 0.00 0.00 0.00 100.00 133.75 +25.98 21.0
06/18/2019 20:08:06 236.88 239.33 0.00 0.00 0.00 0.00 0.00 100.00 134.00 +26.09 21.0
06/18/2019 19:58:06 237.72 240.11 0.00 0.00 0.00 0.00 0.00 100.00 134.28 +26.25 20.0
06/18/2019 19:48:06 239.09 240.50 0.00 0.00 0.00 0.00 0.00 100.00 134.56 +26.42 21.0
06/18/2019 19:38:06 238.67 241.02 0.00 0.00 0.00 0.00 0.00 100.00 134.84 +26.52 21.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:01 AM
Hi
For this I would advise contacting your local customer care centre for troubleshooting.
you can all 0800 111 469 or use this web form https://www.apc.com/ch/fr/support/contact/ask_apc.cfm for French, https://www.apc.com/ch/it/support/contact/ask_apc.cfm for Italian or https://www.apc.com/ch/de/support/contact/ask_apc.cfm
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:01 AM
Hi
For this I would advise contacting your local customer care centre for troubleshooting.
you can all 0800 111 469 or use this web form https://www.apc.com/ch/fr/support/contact/ask_apc.cfm for French, https://www.apc.com/ch/it/support/contact/ask_apc.cfm for Italian or https://www.apc.com/ch/de/support/contact/ask_apc.cfm
Regards
Matt