Smart-UPS VT 30KVA - Power Module Total Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS VT 30KVA - Power Module Total Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

0 Likes
6
2915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

Smart-UPS VT 30KVA - Power Module Total Failure

Hi All,

My company has a Smart-UPS VT 30KVA with XR battery enclosure, which is nearly fully populated with packs. The unit is just over three years old, and has never been loaded to more than 60%

The unit has been in operation without fault in a datacentre environment (with controlled temperature and humidity) for it's entire life. Every 2 weeks it runs a self-test, which has always passed.

A few days ago it seems the power module completely failed. It went into soft bypass, the display went blank, and the remote management card stopped responding. No extraneous power conditions or environmental factors were recorded by our monitoring equipment at the time of the failure.

Fortunately it did not drop the load, and we have now bypassed the UPS completely.

Now the UPS will not power up at all - when given power (via the maintenance panel) is does not respond at all (no lights, no noise, no sign of life of any kind).

This has generally been (remotely) diagnosed by APC tech support as a failure of the power module which, it seems, is almost as expensive to replace as the cost of the entire UPS system.

Does anybody have any experience of this failure? Are there any other options - for instance, can the power module be diagnosed and repaired rather than being totally replaced?

Any advice you can offer would be gratefully received. It seems to me that a system like this, when used in basically ideal conditions, should not suffer a total failure after just 3 years.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • failure
  • power_module
  • replacement
  • smart-ups
  • vt
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
2915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

hi all

I checked website and get too much knowledge from forums.

I am new in APC and today i collected one PAC UPS 30 KVA smart UPS from one client

When i checked its bank voltages are OK but UPS is totall death and no indication.

In this power module number is SUVTPM30KH

i need its manuals for start up and maintenance manual and software.
if any body have then please let me inform by email
subhani_engr1@yahoo.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

Hi All,

My company has a Smart-UPS VT 30KVA with XR battery enclosure, which is nearly fully populated with packs. The unit is just over three years old, and has never been loaded to more than 60%

The unit has been in operation without fault in a datacentre environment (with controlled temperature and humidity) for it's entire life. Every 2 weeks it runs a self-test, which has always passed.

A few days ago it seems the power module completely failed. It went into soft bypass, the display went blank, and the remote management card stopped responding. No extraneous power conditions or environmental factors were recorded by our monitoring equipment at the time of the failure.

Fortunately it did not drop the load, and we have now bypassed the UPS completely.

Now the UPS will not power up at all - when given power (via the maintenance panel) is does not respond at all (no lights, no noise, no sign of life of any kind).

This has generally been (remotely) diagnosed by APC tech support as a failure of the power module which, it seems, is almost as expensive to replace as the cost of the entire UPS system.

Does anybody have any experience of this failure? Are there any other options - for instance, can the power module be diagnosed and repaired rather than being totally replaced?

Any advice you can offer would be gratefully received. It seems to me that a system like this, when used in basically ideal conditions, should not suffer a total failure after just 3 years.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

Here we are:

The APC tech that you previously spoke with was accurate in deducing that the power module is the most probable point of failure and needs to be replaced. The PM could be failed for any number of reasons (PSU fault, etc.) - but any failed component in the PM requires the entire PM be replaced (the VT has very few modular parts). The symptom of the UPS being dark, but not dropping the load, is an indication that the static switch still functions, and is not indicative of a catastrophic UPS failure. However, the PM is the most major component of the UPS as it contains logic, inverters, etc.

The easiest test is to reseat the PM with the UPS is completely bypassed. After reseating, does the UPS startup? If not, a site visit may be in order, or simply replace the PM. Unfortunately, without access to controller logs, NMC logs, etc we can't tell what has caused the PM to fail.

Edit: I would just call into our three-phase tech support team @ 1-800-800-4272 and determine a resolution.

Message was edited by: Erasmus

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:33 AM

Looking into your inquiry with our 3-phase team. Will respond shortly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

Thanks for responding. I did actually try re-seating the power module - I've also done a basic visual inspection of it to look for loose wires, blown components, and the like - but no joy.

One additional question springs to mind - the power module in our UPS is part number OG-SUVTPM30KH. This UPS is a UK one, set to 400v. Does anyone know if the power modules are identical in different regional variants? For example, it seems the US region version of the power module has the same part number. Do the internal electronics adjust to different input voltages, or do I need to specifically get a UK power module?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

You would need to contact Europe/EMEA support for the correct power module. The North American model PM is 208v.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:24 AM . Last Modified: ‎2024-03-19 01:32 AM

hi all

I checked website and get too much knowledge from forums.

I am new in APC and today i collected one PAC UPS 30 KVA smart UPS from one client

When i checked its bank voltages are OK but UPS is totall death and no indication.

In this power module number is SUVTPM30KH

i need its manuals for start up and maintenance manual and software.
if any body have then please let me inform by email
subhani_engr1@yahoo.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore